This can be done with kitControl math blocks and a little help from excel's Trendline feature. Copy and paste the temperature vs pressure values in to excel. Convert to PSIA and Deg R (curve fitting works better). Create a graph and try the various Trendlines until you get a good fit. I came up with this for R134a. y = 0.00003561 x^3 - 0.01308796 x^2 + 2.12259171 x + 421.11910836 With x = PSIA and a range of 20.7 to 149.7 and y = deg R.
UA LU 562
-
01-24-2013, 10:50 PM #15
Could I get a copy of the program objects also, email is in my profile, Thank you.
-
01-25-2013, 02:17 AM #161 + 1 = 3 ( *** for very large values of 1)
...everybody wants a box of chocolates and long stemmed rose
-
01-27-2013, 10:42 AM #17
Professional Member
- Join Date
- Jun 2009
- Location
- StL, MO
- Posts
- 532
Thanks. For 134a:
y = 9.20621E-10 x^5 - 6.26875E-07 x^4 + 1.65989E-04 x^3 - 2.26106E-02 x^2 + 2.14070E+00 x - 1.32707E+01
Input pressure range (PSIA) 14.7 to 244.7. Output °R. This turns out to be quite a good fit with R squared = 0.9999Last edited by DaveCR; 01-27-2013 at 10:44 AM. Reason: punctuation
UA LU 562