Niagara AX- Need a Pressure Temperature Conversion block
Does anyone have refrigerant pressure temperature logic blocks or something they can share with me? I need to control exv's from superheat directly in the jace. I was trying to play around with writing something in the program editor but my skill level is not up to par with line by line code.
-
Can you just use a PID those work well in kit control. Or a reset??
-
Yea I am going to use a pid but I need the chart to know what the superheat is. I would need 50 reset blocks to try to make this so I'd rather write a custom module
-
Any suction pressure transducers?? Suction line temp?? This could all help. R-22?? 410??
-
I have a program object for R22.
Go Rangers!
-
Lane I would be interested in that program too
Thanks
Kevin
Email in my profile
Sent from my DROID RAZR using Tapatalk 2
"There is plenty of room at the top because very few people care to travel beyond the average route. And so most of us seem satisfied to remain within the confines of mediocrity." -- Benjamin Nnamdi Azikiwe, first president of Nigeria
"It's not the customer's job to know what they want." -- Steve Jobs
-
Shoot me an email and I will send it to you. It took me forever to find the right equation for this and then when I did I had trouble getting it in the program object and functioning correctly. I have to give the final credit to Ron aka Codewriter for getting it completed for me. You can set the input to PSIG,PSIA, or KPA.
Go Rangers!
-
 Originally Posted by lwarren
I have a program object for R22.
PV=mRT ... hmm would like a look at the program object too if poss.
1 + 1 = 3 ( *** for very large values of 1)
...everybody wants a box of chocolates and long stemmed rose
Be brave. You cannot get eaten by an imaginary tiger.
-
I would be interested in a copy as well.
tia
-
I don't see your email listed Matrix. Whoever wants it just send me an email.
Go Rangers!
-
 Originally Posted by Norriski Tech
Any suction pressure transducers?? Suction line temp?? This could all help. R-22?? 410??
yes i have suction pressure transducers and suction line temp. This is r134, but i can take the r-22 table and edit all the values to change it to 134.
-
I would appreciate a copy, thank you.
-
Me too, I would appreciate a copy of this program object. Thank you!