01-05-2013, 09:55 PM #14
-
01-05-2013, 10:35 PM #15
Regular Guest
- Join Date
- May 2012
- Location
- MD
- Posts
- 32
I have a masters in electrical angering worked in aerospace for over 30 years, I think I can understand a "one wire" electrical circuit.
Looking at my CB panel water heater 10 3, pool pump 10 3, oven 10 3, cook top 10 3, dryer 10 3, compressor 8 3 back up heat 6 3, just saying.
-
01-05-2013, 10:47 PM #16
there is no water heater that is 10/3 so try again... just saying
it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair
-
01-05-2013, 10:52 PM #17
You must be counting the ground as a conductor. 10/2 with ground has 2 insulated conductors and 1 bare copper ground wire, 10/3 with ground has 3 insulated conductors and 1 bare copper ground wire. If they used 10/2 with no ground (like old cloth sheathed wire) then they should have changed the wire to 10/2 with ground.
-
01-07-2013, 09:31 AM #18
Regular Guest
- Join Date
- May 2012
- Location
- MD
- Posts
- 32
I’m not counting the ground I know the difference between 10 2 and 10 3.
My water heater is connected to a disconnect panel and a demand response unit they used 10 3 from the main breaker panel to the disconnect panel.
They used 10 2 Romex for the new fan coil, the circuit was previously used for the old condenser.
The old condenser seized, I think the technician damaged the breaker trying to get the old compressor to turn on, he reset it numerous times, eventually it stopped tripping and started making a loud buzzing noise.
I replaced the breaker on Saturday, I’m still waiting for the installer to come out and check the system.
-
01-07-2013, 01:48 PM #19
Regular Guest
- Join Date
- May 2012
- Location
- MD
- Posts
- 32
The technician came out checked the wiring and ran the electric heat test, but never checked the current draw.
He asked if the breaker tripped why isn’t there a voltage fault? I asked said how can if register a fault if the unit isn’t getting any power.
I noticed the fan coil has two 60 amp breakers but the unit is fed by a 60 amp circuit and a 30 amp circuit the fan coil has a 10K and a 5K electric heater pack.
Shouldn’t the 5k heater pack have a 30 amp breaker not a 60 amp?
It's the 30 amp breaker on my load center that is tripping.Last edited by ATC USN; 01-07-2013 at 01:49 PM. Reason: grammer
-
01-10-2013, 02:06 PM #20
Regular Guest
- Join Date
- May 2012
- Location
- MD
- Posts
- 32
My dealer replaced the heater pack, the problem was a 8 inch section of coil was stretched out and tangled, looks to me like it got snagged during installation.



Reply With Quote