Results 1 to 13 of 20
    May 2012
    MD
    Infinity Fan Coil Breaker Tripping
    The breaker for my Fan Coil keeps tripping, it has happened at least six times since the system was installed in May 2012.
    Because it's the breaker is for the Fan Coil no faults are being recorded, but as best as I can tell it happening when the blower is running on high.
    My system has three breakers 60 amp for Backup Heat a 40 Amp for the Condenser and a 30 amp for the Fan Coil.
    The system passes the electric heat test and the heat pump test and the without tripping the breaker.
    Carrier 25HNB648 Condenser
    Carrier FE4ANB005 Fan Coil
    May 2009
    Savannah, Ga/H.H. Island, S.C.
    Call a professional. Don't reset the tripped breaker again without having it looked at. It is tripping for a reason...a potentially dangerous/hazardous reason.
    There could be several things going on with your system. Call a contractor and let them have a look. If you need help finding a local company, check our contractor locator map.
    But whatever you do, do not keep resetting the breaker. You could injure yourself, your family, or your equipment.
    Lancaster PA
    Should still be under first year labor warranty, so call the contractor to come out.
    i would ave them come out and check it if no problems are found they need to replace the breaker
    May 2012
    MD
    Today I replaced the 30 Amp 2 pole breaker only to find that the installer used 10-2 romex instead of 10 3, there's no neutral wring going to the unit. However there is a neutral wire going to the unit on the 60 Amp circuit.
    The reason I decided to replace the breaker is because originally the circuit was used for the old condenser that has seized the technician tripped it numerous times while troubleshooting the old system.
    The installer will be out on Monday.
    you need a ground not a neutral should be 10/2 with ground wire
    May 2012
    MD
    It's a 2 pole 30 amp circuit breaker it should be 10 3 with a ground they hooked the white wire to one of the poles on the breaker then wrapped it in black tape.
    My system has 3 240 VAC 2 pole breakers, a 30 amp to the fan coil, a 60 amp for electric heat, and a 40 amp to the condenser.
    Anderson SC
    All you need is a 10/2 with ground (white=120v, black=120v, bare copper=ground)
    Apr 2012
    winnipeg
    a 2 pole 30 amp breaker requires..... 10/2
    Nov 2012
    Tahlequah OK
    Your 240 Volt system does not require a neutral. White wires are not always a neutral wire.
    Apr 2012
    winnipeg
    Quote Originally Posted by welling service View Post
    well said.....
    May 2012
    MD
    Quote Originally Posted by carmon View Post
    well said.....
    I didn't know that was still allowed, the cable run is 20' long how much did they save by doing that?
    The breaker hasn't tripped since I replace it.
    Dealer still coming out on Monday.
    Nov 2009
    Kansas City
    Electricity is not a guessiing game. People that don't understand it should leave it alone
