Results 1 to 13 of 20
01-04-2013, 04:11 PM #1
- May 2012
- MD
- 32
Infinity Fan Coil Breaker Tripping
The breaker for my Fan Coil keeps tripping, it has happened at least six times since the system was installed in May 2012.
Because it's the breaker is for the Fan Coil no faults are being recorded, but as best as I can tell it happening when the blower is running on high.
My system has three breakers 60 amp for Backup Heat a 40 Amp for the Condenser and a 30 amp for the Fan Coil.
The system passes the electric heat test and the heat pump test and the without tripping the breaker.
Carrier 25HNB648 Condenser
Carrier FE4ANB005 Fan Coil
01-04-2013, 04:21 PM #2
Call a professional. Don't reset the tripped breaker again without having it looked at. It is tripping for a reason...a potentially dangerous/hazardous reason.
There could be several things going on with your system. Call a contractor and let them have a look. If you need help finding a local company, check our contractor locator map.
But whatever you do, do not keep resetting the breaker. You could injure yourself, your family, or your equipment.
01-04-2013, 06:08 PM #3
Should still be under first year labor warranty, so call the contractor to come out.
01-04-2013, 07:21 PM #4
Professional Member*
- Jul 2006
- Virginia
- 3,716
i would ave them come out and check it if no problems are found they need to replace the breaker
01-05-2013, 07:28 PM #5
- May 2012
- MD
- 32
Today I replaced the 30 Amp 2 pole breaker only to find that the installer used 10-2 romex instead of 10 3, there's no neutral wring going to the unit. However there is a neutral wire going to the unit on the 60 Amp circuit.
The reason I decided to replace the breaker is because originally the circuit was used for the old condenser that has seized the technician tripped it numerous times while troubleshooting the old system.
The installer will be out on Monday.
01-05-2013, 07:32 PM #6
- Jul 2006
- Virginia
- 3,716
you need a ground not a neutral should be 10/2 with ground wire
01-05-2013, 08:36 PM #7
- May 2012
- MD
- 32
It's a 2 pole 30 amp circuit breaker it should be 10 3 with a ground they hooked the white wire to one of the poles on the breaker then wrapped it in black tape.
My system has 3 240 VAC 2 pole breakers, a 30 amp to the fan coil, a 60 amp for electric heat, and a 40 amp to the condenser.
01-05-2013, 08:47 PM #8
All you need is a 10/2 with ground (white=120v, black=120v, bare copper=ground)
01-05-2013, 08:47 PM #9
a 2 pole 30 amp breaker requires..... 10/2
01-05-2013, 08:48 PM #10
- Nov 2012
- Tahlequah OK
- 131
Your 240 Volt system does not require a neutral. White wires are not always a neutral wire.
01-05-2013, 08:53 PM #11
01-05-2013, 09:22 PM #12
- May 2012
- MD
- 32
01-05-2013, 09:45 PM #13
- Nov 2009
- Kansas City
- 114
Electricity is not a guessiing game. People that don't understand it should leave it alone