    refrigerant R-123 leak detectors

    Gentleman : Happy New Years !!!! I have been given a new Christmas present from our contract employeer , we work on low pressure R-123 systems , 2 York YT and CVHF Tranes my question is we have been given a leak detector Reed C-380 and was wondering if anybody had used these units and if so how did you find they worked ?????????? aside from these units , what do you recommend .
    Any input would be greatly appreciated , thanks in advance.

  2. #2
    Join Date
    Jan 2011
    Posts
    1,151
    I haven't tried that particular leak detector, but I have tried plenty of others. I still come back to the Bacharach H-10G. IMO it is the best leak detector on the market.

  3. #3
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    2,036
    I didn't know that the H-10 was now made (or marketed) by Bacharach. I've used, and seen others use, other detectors, but the H-10 is the only one I've ever spent company money on. If I was buying a detector with my money, this is the only one I would buy. The majority of my career has been working on low pressure. Mostly R11, R123, and a few R113 chillers. I've also used it numerous times with R12, R22, and R134a. Oh, and a Happy New Year to you too, Troy!

  4. #4
    Join Date
    Mar 2007
    Posts
    3,108
    3rd vote for the H-10. I used junky cordless battery powered detectors by many different manufacturers for years and I was convinced to purchase an H-10 when a co-worker found a leak on the thrust bearing cover on a centravac with one, and the detector I was using at the time did not so much as chirp. Made me think back about all the machines I had leak checked in the past and how many leaks I have probably missed...
    "There is no greater inequality than the equal treatment of unequals."

    -Thomas Jefferson

  5. #5
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,045
    Another vote here for the H10 ....but........ I only use it as a guide . If it chirps then I go somewhere else then back to the suspect spot several times before reaching for the liquid Snoop .....no bubbles no troubles .
    The 64 roars to life Whoo hoo ...shes a rolling chassis .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  6. #6
    Join Date
    Dec 2012
    Location
    Hamilton Ontario Canada
    Posts
    103
    Gentleman : I appreciate the info and believe without a doubt H-10 is the unit I want , problem we had yesterday and just cause Healey Nut mentioned liquid snoop , we thought we had found some leaks and then tried to find to find them with fluorescent leak detector but then found the electronic leak detectors now picks up the leak detector soap , so I guess my question is does the leak detector not pick up the liquid snoop or is that just a common problem with all leak detector soaps or is there a product that doesn't create a false reading after using it and is there a residue effect after the leak detector soap is used to create more false readings .
    Again as I always say I appreciate your time and expertise in answering my many questions.

  7. #7
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,045
    Quote Originally Posted by Troy Love View Post
    Gentleman : I appreciate the info and believe without a doubt H-10 is the unit I want , problem we had yesterday and just cause Healey Nut mentioned liquid snoop , we thought we had found some leaks and then tried to find to find them with fluorescent leak detector but then found the electronic leak detectors now picks up the leak detector soap , so I guess my question is does the leak detector not pick up the liquid snoop or is that just a common problem with all leak detector soaps or is there a product that doesn't create a false reading after using it and is there a residue effect after the leak detector soap is used to create more false readings .
    Again as I always say I appreciate your time and expertise in answering my many questions.
    Ive tried all those fancy fluorescent soaps and clinging soaps and all the other gimmicks they try with leak detector soaps . Snoop works period and doesnt leave a soapy waxy residue behind it just dries up and its gone .
    I got turned onto Snoop a few years back when I was working at a plant on a recip chiller having leak issues , had nitrogen test in the chiller no residue gas so was just using soap , couldnt find the leak ran out of regular blue soap . Guy at the plant said here try this and found the leaks in no time . Some of the soaps are just too goopy snoop is just water with a surfactant in it thats why it works so well on natural gas leaks, it bubbles instantly even at very low pressure .
    H10 and Snoop all the way for me now , low pressure high pressure it dont matter leaks cant hide from Snoop .
    The 64 roars to life Whoo hoo ...shes a rolling chassis .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  8. #8
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,314
    I'm another vote on the H-10 and snoop. The H-10 is so powerful it will pick up on the smallest leaks (1/2 oz. per year). That's why I follow up with the snoop. On a larger machine, if the leak is not large enough to bubble up the snoop, I'm not going to wast my time trying to repair it. If its a very small machine, like the refrigerant circuit on a purge that holds 6 oz. refrigerant, I will repair it just off the H-10.

  9. #9
    Join Date
    Jan 2008
    Location
    windy city
    Posts
    4,430
    H10.
    and, I just picked up the battery powered version. H10Pm. Pleasantly surprised
    \m/
    original member of the racoon brotherhood

  10. #10
    Join Date
    Mar 2005
    Posts
    664
    what does snoop cost?
    Keep it simple to keep it cool!

  11. #11
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,330
    what is snoop.....
    it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair

  12. #12
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,045
    Its a swagelock product and its cheap .

    http://www.swagelok.com/products/lea...-detector.aspx
    The 64 roars to life Whoo hoo ...shes a rolling chassis .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  13. #13
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,330
    thanks...newer seen it before..... is it good.....
    it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event