    Quote Originally Posted by wdshea View Post
    whats the subcooling? whats the temp. diff across the filter drier? whats the temp. diff. across the king valve? if you think there is a restriction there, i would check for refrigeration effect.

    another trick i've learned from a guy, was to run the condenser, but disconnect the fan control. watch the distribution tubes (in the evaporator) and make sure they all ice up evenly. if one doesn't ice up (or ices up slowly), it's not getting refrigerant.

    only do that with a txv...

  2. #15
    Join Date
    Dec 2010
    Location
    Somewhere in Cali
    Posts
    172
    Check of any temperature drop before and after the liquid line filter.