Results 1 to 13 of 15
    Sep 2010
    miami,fl.
    restriction or low charge
    york 3 ton split system straight cool. 1 tech was at the house earlier in the day said he added gas and low side wont come up above 45ish. with high superheat sounded like low charge or restriction. i stop by on the way home its night time. i didnt want to waste much time i pumped down the unit checked orifice ( no txv) clean inlet screen is clean. i blew liquid line and suction line with nitro since i had it open. pulled vacuum. started the unit back up. same thing. pressures were 45/150. i tried adding gas seems like the low side valve core was messed up. it was taking the charge real slow. got the pressures up to 60 low side 170 hi psig.
    liquid line temp was 73 degrees out door temp 73 degrees,i see inside the condenser there is a copper filter dryer. based on subcooling and liquid line temp im leaning towards a restriction. the only place left it could be is in the high side king valve or filter dryer in the condenser. or the system has a leak im planning on recovering the charge. removing dryer install new outside condenser and gas her back up. hopefully blow through the dryer and find it to be clogged. any input by the way its an r22 system. if more info needed ask me if i have the answers ill input thanks
    Sep 2011
    whats the subcooling? whats the temp. diff across the filter drier? whats the temp. diff. across the king valve? if you think there is a restriction there, i would check for refrigeration effect.
    another trick i've learned from a guy, was to run the condenser, but disconnect the fan control. watch the distribution tubes (in the evaporator) and make sure they all ice up evenly. if one doesn't ice up (or ices up slowly), it's not getting refrigerant.
    Apr 2012
    winnipeg
    oh my....
    Oct 2011
    Chicagoland Area
    Quote Originally Posted by carmon View Post
    oh my....
    Lions and tigers and bears....
    Jul 2000
    Northern Wisconsin
    When you pull the charge, weigh it and check it against the suggested amount. I'd also stabalize the tank temp and check the pressure against the chart for refrigerant specified.
    Jan 2013
    Central, FL
    A restriction anywhere in the liquid line will show a temperature drop if there is any liquid in the system. That will be the clue you need.
    Mn the state where absolutey nothing is allowed
    you know 1/2 the ac is inside the house. why are you looking outside
    not saying, just sayin
    my boss thinks its possible to repeal the laws of physics
    In a boiler room
    Quote Originally Posted by Ductfisher View Post
    Not if the subcooling is high before the restriction. It is possible to have a significant pressure drop across a restriction but have no temp drop.
    Anthony, I think you are on the right track with the restriction. I would bet on that copper drier in the unit.
  9. Likes mixsit liked this post
  10. #9
    what does the filter and indoor coil look like .
    Thank God Trump Won
  11. #10
    Jan 2013
    Central, FL
    I stand corrected. After rerreading this thread I say it is under charged. What is the TD across the coil?
  12. #11
    Sep 2010
    miami,fl.
    well i went to the house today saturday customer wasnt home so i weighed my tank empty recovered gas removed the liquid dryer from inside the condenser, dryer was slightly restrictive i dont think was the root cause but glad i removed it. i recovered 9lbs and compared to the factory charge on cond. nameplate, said 9lbs 1 oz. the end result it has a leak beacause i had added about 3lbs when i went there thursday night. so that tells me originally it was low on charge. customer arrived home as i was cleaning up after dumping the gas back into the system. i went inside the house and the leak detector was going off in the finned area of the coil. and wouldnt stop turned detector off waited about 5 mins turned it back on once i went back to the same spot it went crazy i usually like to spot the leak to confirm but ima conclude its in the coil. i wanted to get back and say the out come i appreciate your input.
  13. #12
    Jul 2012
    central VA
    Leaky evap coils are famous these days
    I rather do nothing and be happy than to do something and not be happy
  14. #13
    Jul 2011
    lmao, this a joke thread right? unit has a piston, and at no point in the OP's thread did he mention his wb or ambient temp, to determine, what he or she needed to determine the superheat...
    scary **** man... Talking about a restriction without determining if the unit is even at the right charge, and totally just nuked it in the end, but reclaiming the refrigerant LOL...
    Not trying to be mean, but read some books bro...
    if both sides of your gauges went up chances are its not a restriction, if you were charging it up... Also what was the compressor amps, etc, etc...
    temp at the compressor discharge and temp at the furnace/air handler at discharge.. LOL
    as I said read books, bro.. Most comments were snive comments at ya...