    Confused Wire Gauge, RLA and LRA.

    I have a compressor motor for a new Geothermal Unit. I need to run a new electrical line.

    16.7 RLA. 82 LRA.

    If I go by the 16.7 RLA, with 20% "extra", I get 20.04 AMPS. That leads me to think 12 gauge wire based on internet searching.
    I'm ok getting 10 gauge.

    220 Volts. It's a crawl space in NC, and not in the attic or something (hot).

    The run is about 23 feet.

    The high number ("82") on the LRA has me a little worried.

    Any confirmation? Or correction?

    Thanks in advance.

  2. #2
    Join Date
    May 2006
    Location
    Philadelphia, PA
    Posts
    3,039
    Post Likes
    The manufacturer will have a spec on this. What does your installer suggest?
    Climate Control Solutions for your Home or Office

    Serving Northeast Philadelphia and Surrounding Areas

  3. #3
    Join Date
    Jan 2013
    Posts
    2
    Post Likes
    Thread Starter
    Quote Originally Posted by comfortdoc View Post
    The manufacturer will have a spec on this. What does your installer suggest?
    He wants to call an electrician and outsource it. Thus why I'm trying to do the physical part of it (run the wire through the crawl space).

    I'm tapped out, getting this system in$talled.

  4. #4
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    the unit should have the minimum circuit amps stamped on the data plate also gives a min and max fuse size . this info is also on the engineering specifications

  5. #5
    Join Date
    May 2008
    Location
    Missouri
    Posts
    4,384
    Post Likes
    We cannot assist with DIY projects. Against the rules for this site. If you don't know what you're doing, call a professional. Good luck!

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •