Results 1 to 6 of 6
    Feb 2007
    American Standard 401 Thermostat "Waiting"
    We usually use a 3 degree setback, but when we hit the $ key to go back to the regular set point the heat pump comes on but "waiting" is illuminated and stays on for perhaps a half hour or so before the system brings the heat strips on line. The installing company insists that in the absence of an outdoor thermostat it is just a system quirk with which I'll have to live. It ISN"T a serious problem as the heat runs and strips do eventually come on, but I was wondering if there was a "workaround". The only setup step in the installer's guide pertains to turning the "waiting" icon on and off; there doesn't appear to be anything that relates to adjusting the "waiting" time.
    Just in case it is relevant:
    4TEE3F337B1000AA Air Handler
    4A6H4036B1000AA Condenser Unit
    BAYTHR1415BRKCB (Heat Strips)
    Aug 2009
    Beatrice, NE
    Sounds to me like you have a bad stat. The "waiting" is just a time delay from the last time the system shut off. If the system just ran it's 5 min., if it ran 4 min ago it's a min delay. If you just turn it on it's 5 min. It should not last 30 min.
    May 2008
    Central Fla.
    If it aint broke, don't fix it. What the company/tech told you sounds good.
    May 2008
    Central Fla.
    KLS, he states the unit runs just the strips are in delay. If you have no O/D stat it will run a predetermined amount of time before the strips come on, this is to see if the pump will satisfy the heat cycle.
    May 2009
    Cumming, GA
    Just to point something out that is totally unrelated to this post.
    TwincamDave, you have the same avatar/profile pic as "toocoolforschool"
    May 2008
    Central Fla.
    Self portrate, shot it with the iphone.HA HA.