r12 refrigerator pressures
Hey guys , new here, usually in residential tech area.... I have an older refrigerator that is not cooling. Why are there 3 tubes coming off the compressor, 2 to the condensor and the third to the evaporator. I put a line tap to check the pressures but don't know what the low side should be. What should the equalized pressure be at ambient 70 F?
THanks
Greg
-
01-02-2013, 11:14 PM #2
Professional Member*
- Join Date
- Nov 2012
- Location
- Tahlequah OK
- Posts
- 131
unknown. Depends on how much R12 is in the system. Is the comp running?
-
01-03-2013, 08:12 AM #3
One of the two into condenser isn't a process stub?
Maybe looks as if going to condenser?
Just a thought!
Pull charge and weigh in with adequate replacement!
sent from my Samsung Galaxy NoteMember of the "Work Exchange Program"
"Will work for knowledge"
"Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
A Einstein
-
01-03-2013, 08:13 AM #4Member of the "Work Exchange Program"
"Will work for knowledge"
"Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
A Einstein
-
01-03-2013, 09:57 AM #5
Look at your PT chart for R12. It holds the answers to your questions.
The pressure at 70ºF should be obvious.
Then think about how a typical domestic refrigerator works and what temperature the evaporator must be to achieve 0ºF to keep your ice cream frozen.
-
01-03-2013, 11:08 AM #6
Regular Guest
- Join Date
- Dec 2011
- Location
- louisiana
- Posts
- 50
compressor is running, was wondering what design low pressure should be, can see a fourth tube that is stubbed off, sorry, not thinking cause I do have a pressure chart so.... 0 degrees for freezer looks like around 9 PSI for evaporator, ambient 70 degrees around 70 PSI. No cool evaporator line on compressor so I can't see any other problem other than low charge, fans working, when I finally got tap in place, about 50 PSI and pulled down to 0 PSI when running.
Thanks for your help
-
01-03-2013, 01:43 PM #7
Professional Member
- Join Date
- Feb 2004
- Location
- Madison, WI
- Posts
- 253
I did appliance repair a long, long time ago and if memory serves you could be looking at an oil cooler. Seems the compressor oil cooling was a small circuit routed through the static condenser, but it should have a return line into the compressor. Look again, are you sure there isn't another tube?
As far as suction side pressures listen to icemeisters advice, but seems self defrost models, R-12 would typically run around 3 lbs and manual defrost types would be a little higher, like 6 or 7 lbs.
-
01-03-2013, 03:56 PM #8
-
01-03-2013, 05:01 PM #9