Gas valve with rectifiers
Had a service call today on a Carrier roof top M#48TMF012---501HQ. Found unit locked out on failed ignition (gas valve would not open with 24V). Replaced valve and checked operation. OK. The new valve (White Rodgers 36H54) was an excact replacement and came with a wiring diagram that showed rectifiers inside the valve. Does anybody know why there would be rectifiers on gas valve? Also when I removed the common wire from the valve when the Carrier control/ignition board was in the heating mode, the board would lock out on internal fault (8 flashes). This is the valve http://www.partsguy.com/pdf/36H64-463%20INS.pdf
-
01-02-2013, 08:10 PM #2
Professional Member
- Join Date
- Apr 2006
- Location
- mechanical room
- Posts
- 1,212
probably just a vdc valve
-
01-02-2013, 08:32 PM #3
Maybe I'm missing something.
Are you saying you are surprised that there are rectifiers in the gas valve?[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
01-02-2013, 08:44 PM #4
Are these rectifiers how slow-open or step-open functions are achieved?
-
01-02-2013, 09:11 PM #5
Regular Guest
- Join Date
- Nov 2008
- Location
- Edmonton, Alberta
- Posts
- 6
-
01-02-2013, 09:15 PM #6
Regular Guest
- Join Date
- Nov 2008
- Location
- Edmonton, Alberta
- Posts
- 6
-
01-02-2013, 09:29 PM #7
Professional Member
- Join Date
- Oct 2012
- Location
- La Crosse, WI
- Posts
- 262
The rectifier is to convert the 24vac to dc current, and the coil inside the gas valve is dc. They call it an "internally rectified coil".
I think some water valves in ice machines are the same way.
-
01-02-2013, 10:24 PM #8
-
01-02-2013, 10:34 PM #9
-
01-02-2013, 10:35 PM #10
Professional Member
- Join Date
- Oct 2012
- Location
- La Crosse, WI
- Posts
- 262
DC coil has no inrush when it pulls in. I think they run cooler and draw less current too.
-
01-05-2013, 03:05 PM #11
Professional Member
- Join Date
- Aug 2012
- Location
- Los Angeles
- Posts
- 18
[QUOTE=klubpolo;14901431]Also when I removed the common wire from the valve when the Carrier control/ignition board was in the heating mode, the board would lock out on internal fault (8 flashes). [/URL][/QUOTE
What is the fault for 8 flashes, should be listed on the cover panel, Do you get 8 Flashes immediately? Or dose the unit try unit fail on ignition consecutive times before the 8 flash lock out?
-