Thread: Carrier 7.5 Ton Heat Pump
-
01-01-2013, 03:43 PM #1
New Guest
- Join Date
- Jan 2013
- Posts
- 3
Carrier 7.5 Ton Heat Pump
I have a Carrier 7.5 ton Heat Pump that suffered a severe burnout. I was really careful in the compressor change following all recommendations from Copeland on clean up,etc. It is a Scroll compressor and when I went back to start it up after charging by weight with R-22, the suction went to zero and the head pressure was unchanged,holding steady at 50 psig. The suction pressure goes back to 45 psig when the system is cut off. Cant run it long because I dont want the scroll going into a vacuum I m thinking a blockage somewhere but dont really know where to start. Looking for some other opinons to help me figure out where to begin. This is a 10 year old unit and compressor number 2. Trying to prevent compressor number 3 from occurring.
-
01-01-2013, 04:03 PM #2
Professional Member*
- Join Date
- Dec 2002
- Location
- SouthEast NC ICW & Piedmont Foothills
- Posts
- 7,219
does this thing have a model #?
does it have a solenoid somewhere?
is there a txv?
where did you get the charge weight from?
It`s better to be silent and thought the fool; than speak and remove all doubt. 
-
01-01-2013, 04:24 PM #3
New Guest
- Join Date
- Jan 2013
- Posts
- 3
Model # 38ARQ008-501
Indoor TXV which was replaced about 3 years ago
No solenoid that I know of
Got charge from data plate on unit
-
01-01-2013, 06:23 PM #4
Are you running in heat or cool?
What was the amount the nameplate's calling for? I thought they only had a holding charge listed.
-
01-01-2013, 06:31 PM #5
Commercial equipment is field charged so unless the installer marked the charge (which I wouldn't trust) it is only a holding charge. Packaged units are fully charged though.
-
01-01-2013, 07:04 PM #6
New Guest
- Join Date
- Jan 2013
- Posts
- 3
2.8 lbs r-22 it may be only a holding charge i thought it seemed really low but i cant get the unit to take anymore gas either i thought the low pressure switch would not open if it was too low.
-
01-01-2013, 07:14 PM #7
Professional Member*
- Join Date
- Nov 2012
- Location
- Tahlequah OK
- Posts
- 131
This is a 3 phase unit I assume. Have you checked the rotation? If the suction goes to zero why can't you add more gas? 2.8 pounds is no where near a full charge.
-
01-01-2013, 07:17 PM #8
Professional Member*
- Join Date
- Dec 2002
- Location
- SouthEast NC ICW & Piedmont Foothills
- Posts
- 7,219
1-might want to look around that IDU for a solenoid valve.
2-how long is the piping?
3- suction =0 & head=50?????is that correct?
4-just how much r-22 did you weigh in?
It`s better to be silent and thought the fool; than speak and remove all doubt. 
-
01-03-2013, 09:12 PM #9
New Guest
- Join Date
- Dec 2010
- Location
- Downingtown, PA
- Posts
- 5
Did you also change reversing valve, liquid drier, and contactor?
-
01-05-2013, 11:36 AM #10
Professional Member
- Join Date
- Sep 2006
- Location
- Ohio
- Posts
- 345
Is this a RTU or Split System
-
01-05-2013, 02:36 PM #11
Professional Member
- Join Date
- Aug 2012
- Location
- Los Angeles
- Posts
- 18
-
01-05-2013, 02:39 PM #12
Professional Member
- Join Date
- Aug 2012
- Location
- Los Angeles
- Posts
- 18


Reply With Quote