Thread: Transformer on airhandler (Goodman) keeps burning out the primary side.

  1. #1
    Join Date
    Oct 2009
    Location
    Owasso, OK
    Posts
    43
    Post Likes

    Transformer on airhandler (Goodman) keeps burning out the primary side.

    I've got this Goodman Heat pump that keeps burning up the primary side of the transformer (240V)... Put a new transformer on it and the next morning I get a call that it's not working again. I've seen them blow the secondary side due to low voltage wiring issues but never run across one that does the primary side..... what am I missing.... all the relays (blower, heating element) look good..... what would cause this to be happening...... Electrician came and checked the incoming power and neutrals said everything looks good said I probably just got a lemon transformer..... Any Ideas??

  2. #2
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    How are you checking it to know that it is the primary side that is burning up?
    Training is important!
    Practical Training is a must!

  3. #3
    Join Date
    Jun 2004
    Location
    Eugene, Oregon
    Posts
    1,015
    Post Likes
    Is the secondary side fused?
    "The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin
    "Don't argue with an idiot, they will drag you down to their level and beat you with experience". --Mark Twain
    http://www.campbellmechanical.com

  4. #4
    Join Date
    Jan 2007
    Location
    N.E. Ok.
    Posts
    1,483
    Post Likes
    Did you check the defrost circuit for shorts?

  5. #5
    Join Date
    Dec 2012
    Location
    Daphne, AL
    Posts
    79
    Post Likes
    I've always heard that when the secondary side is grounded, shorted, etc., it will be the primary side that burns. Make sure to fuse your secondary side, so you can find the short without constantly replacing transformers. I'm going to go do a little more research on the first statement I made. See what I can find out.

  6. #6
    Join Date
    Dec 2012
    Location
    Daphne, AL
    Posts
    79
    Post Likes
    Check the archives. There is a long discussion about primary/secondary. It seems to me that what I said above is correct. When the secondary side is over amping, the primary side will be the first to burn. Keep checking the control side for a short or ground. Hopefully it will not be an intermittent ground. Pulled an all nighter on those before.

  7. #7
    Join Date
    Nov 2008
    Location
    baltimore
    Posts
    26
    Post Likes
    Yes, a secondary side short can cause primary coil to burn up. Make sure the secondary side has a fuse on it then see what happens. Loose wire, bad contactor, relay could cause this on a unfused transformer.

  8. #8
    Join Date
    May 2011
    Location
    Ripley, WV
    Posts
    1,607
    Post Likes
    Also get one of these to help out with when troubleshooting.

    http://fierychill.com/lil-popper-3-a...-products-pop3

  9. #9
    Join Date
    Oct 2009
    Location
    Owasso, OK
    Posts
    43
    Post Likes
    Thread Starter
    No the secondary isn't fused so I'll do that and start tracking the 24 v side

  10. #10
    Join Date
    Oct 2009
    Location
    Owasso, OK
    Posts
    43
    Post Likes
    Thread Starter
    Thanks I'll get one for sure

  11. #11
    Join Date
    Oct 2009
    Location
    Owasso, OK
    Posts
    43
    Post Likes
    Thread Starter
    Thanks.... going to check the defrost...... stayed for about 1hr after starting system with the new transformer and everything was fine so it very well could be in the defrost side.

  12. #12
    Join Date
    Oct 2009
    Location
    Owasso, OK
    Posts
    43
    Post Likes
    Thread Starter
    With a meter checking continuity

  13. #13
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Quote Originally Posted by captube View Post
    Did you check the defrost circuit for shorts?
    That would be on the secondary side.
    Training is important!
    Practical Training is a must!

  14. #14
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    I agree that the problem is more likely on the secondary side. An easy way to fuse the transformer is to cut the hot wire from the transformer secondary side, put insulated female spade connectors on both ends of the cut wire and plug a 3 amp automotive fuse into the connectors.
    Training is important!
    Practical Training is a must!

  15. #15
    Join Date
    Dec 2007
    Posts
    13,231
    Post Likes
    could use a new transformer with built in resettable fuse, too.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  16. #16
    Join Date
    Dec 2012
    Location
    Daphne, AL
    Posts
    79
    Post Likes
    I agree with pacnw. I now use a 50va transformer with a resettable fuse. For a few bucks more I get a little safety margin and a resettable secondary fuse. No more manually tieing fuse holders to transformers. Don't know if I am allowed to tell the brand name or not? Somebody let me know if you want brand name.

  17. #17
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    Most times I've found a bad xmfr it was the primary side open or shorted caused by a secondary side short. Bad RV coil is a pretty common cause for lv short.

  18. #18
    Join Date
    Jun 2012
    Posts
    39
    Post Likes
    Make sure you check the wiring outside especially around the wire ties

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •