01-02-2013, 08:53 PM #14
I agree that the problem is more likely on the secondary side. An easy way to fuse the transformer is to cut the hot wire from the transformer secondary side, put insulated female spade connectors on both ends of the cut wire and plug a 3 amp automotive fuse into the connectors.
Government is a disease......masquerading as its own cureEcclesiastes 10:2 NIV
-
01-02-2013, 10:06 PM #15
could use a new transformer with built in resettable fuse, too.
If Guns Kill People, Do Pencils Misspell Words?
http://www.youtube.com/watch?feature...&v=2kX_3y3u5Uo
http://www.youtube.com/watch?v=JVAhr4hZDJE
http://www.youtube.com/watch?v=-TC2xTCb_GU
-
01-02-2013, 10:22 PM #16
Professional Member
- Join Date
- Dec 2012
- Location
- Birmingham, AL
- Posts
- 37
I agree with pacnw. I now use a 50va transformer with a resettable fuse. For a few bucks more I get a little safety margin and a resettable secondary fuse. No more manually tieing fuse holders to transformers. Don't know if I am allowed to tell the brand name or not? Somebody let me know if you want brand name.
-
01-02-2013, 10:22 PM #17
Most times I've found a bad xmfr it was the primary side open or shorted caused by a secondary side short. Bad RV coil is a pretty common cause for lv short.
-
01-02-2013, 10:32 PM #18
Regular Guest
- Join Date
- Jun 2012
- Posts
- 33
Make sure you check the wiring outside especially around the wire ties