    Transformer on airhandler (Goodman) keeps burning out the primary side.
    I've got this Goodman Heat pump that keeps burning up the primary side of the transformer (240V)... Put a new transformer on it and the next morning I get a call that it's not working again. I've seen them blow the secondary side due to low voltage wiring issues but never run across one that does the primary side..... what am I missing.... all the relays (blower, heating element) look good..... what would cause this to be happening...... Electrician came and checked the incoming power and neutrals said everything looks good said I probably just got a lemon transformer..... Any Ideas??
    Nov 2000
    Eastern PA
    How are you checking it to know that it is the primary side that is burning up?
    ...seek, and ye shall find;..
    Ecclesiastes 10:2 NIV
    Eugene, Oregon
    Is the secondary side fused?
    "The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin
    "Don't argue with an idiot, they will drag you down to their level and beat you with experience". --Mark Twain
    http://www.campbellmechanical.com
    N.E. Ok.
    Did you check the defrost circuit for shorts?
    Dec 2012
    Daphne, AL
    I've always heard that when the secondary side is grounded, shorted, etc., it will be the primary side that burns. Make sure to fuse your secondary side, so you can find the short without constantly replacing transformers. I'm going to go do a little more research on the first statement I made. See what I can find out.
    Dec 2012
    Daphne, AL
    Check the archives. There is a long discussion about primary/secondary. It seems to me that what I said above is correct. When the secondary side is over amping, the primary side will be the first to burn. Keep checking the control side for a short or ground. Hopefully it will not be an intermittent ground. Pulled an all nighter on those before.
    Nov 2008
    baltimore
    Yes, a secondary side short can cause primary coil to burn up. Make sure the secondary side has a fuse on it then see what happens. Loose wire, bad contactor, relay could cause this on a unfused transformer.
    May 2011
    Ripley, WV
    Also get one of these to help out with when troubleshooting.
    http://fierychill.com/lil-popper-3-a...-products-pop3
    Oct 2009
    Owasso, OK
    No the secondary isn't fused so I'll do that and start tracking the 24 v side
    Oct 2009
    Owasso, OK
    Thanks I'll get one for sure
    Oct 2009
    Owasso, OK
    Thanks.... going to check the defrost...... stayed for about 1hr after starting system with the new transformer and everything was fine so it very well could be in the defrost side.
    Oct 2009
    Owasso, OK
    With a meter checking continuity
    Nov 2000
    Eastern PA
    Quote Originally Posted by captube View Post
    That would be on the secondary side.