    How to control Barber-Colman MP-5213-0-0-4

    Guys , Im trying to retrofit a control system in a local school and they used Barber-Colman MP-5213-0-0-4 actuators on some of the Heat/Chilled water valves. Can they be controlled with a 2-10/0-10/4-20 signal or what does it take to control these?

    Thanks in advance!

  2. #2
    Join Date
    Jun 2006
    Posts
    254
    Post Likes
    Most likely 6-9vdc but you also need a capacitor to put between red and blue wires to stabilize the internal 20 Vdc power supply then put control signal + on yellow and common on blue but get the correct document from Schneider before you wire it. I’m just relying on memory.

  3. #3
    Join Date
    Feb 2005
    Posts
    1,724
    Post Likes
    pretty good memory.

    https://s3.amazonaws.com/s3.supplyho...13-product.pdf

    looks like there are a few different models.

  4. #4
    Join Date
    Jan 2003
    Location
    USA
    Posts
    9,437
    Post Likes
    Yuk, the old beer can hydraulic actuators. Its not worth the time to wire them up IMO. Notorious for oil leaking out and failing. Almost every time I have ran into these, its a large percentage that have long ago failed.
    Propagating the formula. http://www.noagendashow.com/

  5. #5
    Join Date
    Dec 2005
    Location
    California
    Posts
    984
    Post Likes
    Unless you get the ones built before they made them in Mexico...Belimo makes a good conversion kit.

  6. #6
    Join Date
    Jun 2009
    Location
    StL, MO
    Posts
    730
    Post Likes
    "When this actuator is used with a DDC controller, it is important to program the controller's output to provide a minimum control span of 4.5 to 11.5 Vdc, to assure full travel to each end of the actuator stroke."


    Since none of the controllers I use have 0-11.5 Vdc outputs, I have been bitten once by that requirement.
    UA LU 562

  7. #7
    Join Date
    Jan 2003
    Location
    USA
    Posts
    9,437
    Post Likes
    It only leaks by a little bit...
    Propagating the formula. http://www.noagendashow.com/

  8. #8
    Join Date
    Feb 2009
    Location
    Northeast
    Posts
    587
    Post Likes
    Yep, when they bleed red blood they are dead.

    We used a JCI actuator on these valves, VA-4233 and a V-9999-BC1 adaptor. But now we mostly replace the whole valve. Packing and seats getting pretty old now. Cut in a ball valve style for less $$ than a new actuator.

  9. #9
    Join Date
    Apr 2019
    Location
    USA USA USA
    Posts
    1
    Post Likes
    Quote Originally Posted by control$ View Post
    Unless you get the ones built before they made them in Mexico...Belimo makes a good conversion kit.
    do you know what the conversion kit was?

    sorry for reviving an oooold thread

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •