    Larkin condensors

    Just throwing this out there for you guys. Over the last year my company has installed 4-5 new walk in coolers. ( evaps, TXV, line sets and cond.)

    And every last one has had a bad headmaster right out of the gate. The latest one is a Larkin m: LHT050X60CFM, new style with the micro channel coil. Once everything is up and running my liquid side hangs about 140PSI on a 180 valve. Check condensor coil and half is warm and half is cool. ( 24lbs of 404-a) Site glass flashing a bit. Add a fan cycler and of course glass clears during fan off. Fan cycles on glass remains clear. Ambient was 30*

    We have done this a few times like I said til we can get a new head master, new valve diverts flow as needed and maintains the 180... Just wondering if anyone else has been having these issues right out of the gate.

  2. #2
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Interesting. What brand valves??

  3. #3
    Join Date
    Mar 2010
    Location
    plano,IL
    Posts
    28
    Post Likes
    Thread Starter
    Sporlan OROA-5-180

  4. #4
    Join Date
    May 2003
    Location
    Utah
    Posts
    921
    Post Likes
    From my experience in working for the valve company in question and being in the industry for nearly 40 years......almost without exception when someone finds multiples of the same component all failing on startup, there is normally some other explanation besides it being a defective component.

    Just saying.....

  5. #5
    Join Date
    Jul 2006
    Location
    Anytown USA
    Posts
    2,257
    Post Likes
    How are you coming up with the additional charge to flood the condenser using the microchannel coil?

  6. #6
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by bunny View Post
    From my experience in working for the valve company in question and being in the industry for nearly 40 years......almost without exception when someone finds multiples of the same component all failing on startup, there is normally some other explanation besides it being a defective component.

    Just saying.....
    This makes a LOT of sense.

    One failure? Yeah, it happens. Multiple failures? Something fishy is going on.

    Quote Originally Posted by y7turbo View Post
    How are you coming up with the additional charge to flood the condenser using the microchannel coil?
    I know that Heatcraft published a chart that just gave a flooding charge value for their microchannel coils.

    I suppose that Larkin would, too.



  7. #7
    Join Date
    Jul 2006
    Location
    Anytown USA
    Posts
    2,257
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post

    I know that Heatcraft published a chart that just gave a flooding charge value for their microchannel coils.

    I suppose that Larkin would, too.
    In sure they do JP. Lets see how the OP calculated the charge.

  8. #8
    Join Date
    Dec 2000
    Location
    Flat Rock, NC
    Posts
    463
    Post Likes
    It does sound like system charge is the culprit. You must charge to full sight glass then add additional chagrge for low ambient operation. If sight glass was not full then there was not enough charge to flood condenser which would then lower condenser pressure below valve setting. I must admit that 24 lb is about what I normally charge that size unit when lines are under 50'.

  9. #9
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    This makes a LOT of sense.

    One failure? Yeah, it happens. Multiple failures? Something fishy is going on.



    I know that Heatcraft published a chart that just gave a flooding charge value for their microchannel coils.

    I suppose that Larkin would, too.
    I thought Larkin was Heatcraft?

  10. #10
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by ryan1088 View Post
    I thought Larkin was Heatcraft?
    I can't keep track of who is who.

    Bohn is Heatcraft, I know.

    Other than that, I write down the numbers and somebody else deciphers who owns who and who supplies what parts.



  11. #11
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    Flashing glass = big red flag.

  12. #12
    Join Date
    Oct 2008
    Location
    Cleveland, Ohio
    Posts
    27
    Post Likes
    Weigh in charge until glass is full. Take that weight and figure out what 10% of that is and weigh that in. Heatcraft tech support told me that 12 years ago and I have done it ever since with out fail.

  13. #13
    Join Date
    Jan 2005
    Location
    where it's nice and warm
    Posts
    359
    Post Likes
    Quote Originally Posted by evilsanta View Post
    Weigh in charge until glass is full. Take that weight and figure out what 10% of that is and weigh that in. Heatcraft tech support told me that 12 years ago and I have done it ever since with out fail.
    Did he tell you what the ambient should be when doing this.

  14. #14
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes

    Re: Charging Heatcraft Condensing Units

    Heatcraft's I & O manuals for their condensing units leave a lot to be desired regarding how to properly charge a system. In addition, their units' data tags don't indicate anything about either receiver capacity or winter charge requirement with a condenser flooding control like some other manufacturers do.

    Just as I had to do some digging to find that PDF on the HyperCore flooding charge info, it took a bit of searching all of their published literature to find any mention of winter charging methods.

    Here's a little ditty from a FAQ page which actually discusses it...in part (Scroll down to near the bottom under "Disadvantages":

    FAQs - Flooded Condenser Using Headmaster

    It states that after the sightglass is cleared add 15% of the initial weighed-in charge for operation down to 0ºF or an additional 30% for -20ºF.

    Bear in mind that these guidelines were written before the advent of the microchannel designs and their vastly reduced coil volumes.

    A more correct method for HyperCore units would be to clear the SG (while maintaining a condensing temperature above 105ºF by blocking airflow as necessary) and add the 2-3 lbs flooding charge as indicated in my previous link.

  15. #15
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Larkin is also Heatcraft. Their nameplates need special deciphering
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  16. #16
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    What's all this talk about 90% receiver capacity?

    Stop it!

    I'll never charge a receiver to 90%.


  17. #17
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by Phase Loss View Post
    What's all this talk about 90% receiver capacity?

    Stop it!

    I'll never charge a receiver to 90%.

    I think that they mean to charge the system to no more than 90% of the receiver's total holding capacity.



  18. #18
    Join Date
    Jul 2005
    Location
    Phoenix, AZ
    Posts
    266
    Post Likes
    Heatcraft owns Bohn, Larkin, Climate Control, and Chandler. Check the flooded charge.

    Sent from my DROID RAZR using Tapatalk 2

  19. #19
    Join Date
    Mar 2010
    Location
    plano,IL
    Posts
    28
    Post Likes
    Thread Starter
    Charge was calculated by size of receiver height and diameter. and mounting direction ( vertical or horizontal) We all have books and literature from united refrigeration and refrigeration research. That will give you the capacity of it. That is how our company and a few of the 20 plus year guys have always said to do it.
    At my previous company I was always told to charge to a til glass.

    I have been hesitant lately of over charging I had one case over the summer that I over charged by about 6lbs and got a call back on the WIF not holding temp. But that was charging til a clear glass and it bit me.

    So now Ive been trying to use as literature as possible when charging. I also do agree with you guys that once ok but multiple times odds are that it is more than likely not a equipment issue. But everything was installed and charged to the letter so that is the part that makes it odd. and when a new headmaster is installed everything acts properly.

  20. #20
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    And I believe Lennox owns Heatcraft
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •