    Just throwing this out there for you guys. Over the last year my company has installed 4-5 new walk in coolers. ( evaps, TXV, line sets and cond.)
    And every last one has had a bad headmaster right out of the gate. The latest one is a Larkin m: LHT050X60CFM, new style with the micro channel coil. Once everything is up and running my liquid side hangs about 140PSI on a 180 valve. Check condensor coil and half is warm and half is cool. ( 24lbs of 404-a) Site glass flashing a bit. Add a fan cycler and of course glass clears during fan off. Fan cycles on glass remains clear. Ambient was 30*
    We have done this a few times like I said til we can get a new head master, new valve diverts flow as needed and maintains the 180... Just wondering if anyone else has been having these issues right out of the gate.
    Mar 2009
    Mid-Mo
    Interesting. What brand valves??
    Mar 2010
    plano,IL
    Sporlan OROA-5-180
    May 2003
    Utah
    From my experience in working for the valve company in question and being in the industry for nearly 40 years......almost without exception when someone finds multiples of the same component all failing on startup, there is normally some other explanation besides it being a defective component.
    Just saying.....
    Anytown USA
    How are you coming up with the additional charge to flood the condenser using the microchannel coil?
    Quote Originally Posted by bunny View Post
    Just saying.....
    This makes a LOT of sense.
    One failure? Yeah, it happens. Multiple failures? Something fishy is going on.
    Quote Originally Posted by y7turbo View Post
    I know that Heatcraft published a chart that just gave a flooding charge value for their microchannel coils.
    I suppose that Larkin would, too.
    Dec 2000
    Flat Rock, NC
    It does sound like system charge is the culprit. You must charge to full sight glass then add additional chagrge for low ambient operation. If sight glass was not full then there was not enough charge to flood condenser which would then lower condenser pressure below valve setting. I must admit that 24 lb is about what I normally charge that size unit when lines are under 50'.
    Mar 2009
    Mid-Mo
    I thought Larkin was Heatcraft?
    Jul 2012
    Western KY
    Flashing glass = big red flag.
    I can't keep track of who is who.
    Bohn is Heatcraft, I know.
    Other than that, I write down the numbers and somebody else deciphers who owns who and who supplies what parts.
    Anytown USA
    In sure they do JP. Lets see how the OP calculated the charge.
    Oct 2011
    Chicagoland Area
    Larkin is also Heatcraft. Their nameplates need special deciphering
    Jul 2005
    Phoenix, AZ
    Heatcraft owns Bohn, Larkin, Climate Control, and Chandler. Check the flooded charge.