Results 1 to 13 of 17
Thread: Honeywell T8011R 1006
01-01-2013, 05:02 PM #1
Professional Member*
- May 2007
- Central NJ Area
- 630
Has anyone had any problems with this heatpump thermostat?
Does anyone have a wiring diagram? The honeywll install manual is horrrible.
I hooked up WHITE wire top W and Aux terminal, yellow to Y, orange to O, green to g, red to R. Is this basically correct for normal hook up to heat pump with aux heat? Is there a installation mode where settings can be changed? Their is no mention of it in the manual.
Thanx
01-01-2013, 05:31 PM #2
White wire if its your aux heat goes to W2. A jumper from W1 to Y is needed for heat pumps.
Haven't used one of those Pieces Of Science for a while. As I recall, you have to set the temp to 52 and then hold the up and down arrows to enter installer set up. Limited abilities.
01-01-2013, 08:24 PM #3
- May 2007
- Central NJ Area
- 630
01-01-2013, 09:12 PM #4
I think you mean E to W2.
01-01-2013, 10:36 PM #5
- May 2007
- Central NJ Area
- 630
02-01-2013, 11:38 AM #6
Are we talking here about Vision Pro 8000. Tstat? Two stage heat and one cooling. Press sceadule and second and fourt blank area. Now you are in installer setup mode. O terminan wire from tstat goes to oO terminal at the pump. W1 is for electric or emergency heat. Make shure in installer set up you choose reversing valve O terminal energized in cooling mode
Sent from my SGH-T999 using Tapatalk 2
02-01-2013, 12:32 PM #7
02-01-2013, 01:09 PM #8
02-01-2013, 01:14 PM #9
02-01-2013, 01:32 PM #10
I see now, my bad.....and sorry. I did not realise that is said T8,. Thinkig of TH800,TH811,TH832OU. Those tstats have same way to get to installer set up. I was WRONG.
02-01-2013, 01:45 PM #11
02-01-2013, 01:56 PM #12
There is a good app on Appstore IOS.....called RTFM thermostats, with preloaded instal and operating manuals for hundreds of different brandsand models. Easy to use and well orginised. It will make you look smarter than average tech.......
02-01-2013, 04:55 PM #13