    Confused Carrier 7.5 Ton Heat Pump

    I have a Carrier 7.5 ton Heat Pump that suffered a severe burnout. I was really careful in the compressor change following all recommendations from Copeland on clean up,etc. It is a Scroll compressor and when I went back to start it up after charging by weight with R-22, the suction went to zero and the head pressure was unchanged,holding steady at 50 psig. The suction pressure goes back to 45 psig when the system is cut off. Cant run it long because I dont want the scroll going into a vacuum I m thinking a blockage somewhere but dont really know where to start. Looking for some other opinons to help me figure out where to begin. This is a 10 year old unit and compressor number 2. Trying to prevent compressor number 3 from occurring.

  2. #2
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    8,494
    Post Likes
    does this thing have a model #?

    does it have a solenoid somewhere?

    is there a txv?

    where did you get the charge weight from?
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  3. #3
    Join Date
    Jan 2013
    Posts
    3
    Post Likes
    Thread Starter
    Model # 38ARQ008-501
    Indoor TXV which was replaced about 3 years ago
    No solenoid that I know of
    Got charge from data plate on unit

  4. #4
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    Are you running in heat or cool?

    What was the amount the nameplate's calling for? I thought they only had a holding charge listed.

  5. #5
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    Commercial equipment is field charged so unless the installer marked the charge (which I wouldn't trust) it is only a holding charge. Packaged units are fully charged though.

  6. #6
    Join Date
    Jan 2013
    Posts
    3
    Post Likes
    Thread Starter
    2.8 lbs r-22 it may be only a holding charge i thought it seemed really low but i cant get the unit to take anymore gas either i thought the low pressure switch would not open if it was too low.

  7. #7
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    Post Likes
    This is a 3 phase unit I assume. Have you checked the rotation? If the suction goes to zero why can't you add more gas? 2.8 pounds is no where near a full charge.

  8. #8
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    8,494
    Post Likes
    1-might want to look around that IDU for a solenoid valve.

    2-how long is the piping?

    3- suction =0 & head=50?????is that correct?

    4-just how much r-22 did you weigh in?
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  9. #9
    Join Date
    Dec 2010
    Location
    Downingtown, PA
    Posts
    7
    Post Likes
    Did you also change reversing valve, liquid drier, and contactor?

  10. #10
    Join Date
    Sep 2006
    Location
    Ohio
    Posts
    798
    Post Likes
    Is this a RTU or Split System

  11. #11
    Join Date
    Aug 2012
    Location
    Los Angeles
    Posts
    18
    Post Likes
    Quote Originally Posted by heat fixer View Post
    2.8 lbs r-22 it may be only a holding charge i thought it seemed really low but i cant get the unit to take anymore gas either i thought the low pressure switch would not open if it was too low.
    Sounds like the unit has a LOW charge, 2.8 lbs R22 is way low on a 88,000 BTU unit.
    The Data sticker reads 2.8lbs R22 that is the charge the unit was shipped with, the Normal operating charge is around 20lbs.

  12. #12
    Join Date
    Aug 2012
    Location
    Los Angeles
    Posts
    18
    Post Likes
    Quote Originally Posted by welling service View Post
    This is a 3 phase unit I assume. Have you checked the rotation? If the suction goes to zero why can't you add more gas? 2.8 pounds is no where near a full charge.
    You have to charge the unit wile it is running on the suction side. Be Cautious not everyone can do this....

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •