01-01-2013, 04:19 PM #27
Professional Member*
- Join Date
- Dec 2002
- Location
- SouthEast NC ICW & Piedmont Foothills
- Posts
- 7,219
if that pressure switch has the +/- or the rating on it; count your blessings---wait until you have to deal with carrier and their mystery pressure switches.
just took a stab in the dark with that pdf's model #, by and large the procedure for checking doesn't change based on model #
It`s better to be silent and thought the fool; than speak and remove all doubt. 
-
01-01-2013, 08:23 PM #28
Professional Member
- Join Date
- Jan 2007
- Location
- Mn the state where absolutey nothing is allowed
- Posts
- 1,097
dude, you installed the wrong pressure switch and now you think it works???. let me ask you something. what did you do to determine that the switch was in fact defective?. it is a safty device . maybe it was actually doing its job!
if it was doing its job and you got it to run with the wrong switch.. just how do you know the furnace is running safe?
pls report back with the switch rating and what your manometer read when you measured the pressure.
to borrow NCI's line.. if your not measuring, your just guessing.
just guessing on a safty device is just plain stupidLast edited by ch4man; 01-01-2013 at 08:45 PM.
my boss thinks its possible to repeal the laws of physics
-
01-01-2013, 08:47 PM #29
Is it a g26? I had one were the header box came apart and didn't have any differential in pressure. This was the first one I dealt with just like you and it took awhile for me to figure it out being That I was pretty green. Sometimes you just have to tear things apart and see what's going on or use your manometer, that's why you own one right? So anyways the way they work is simple you have 2 negative pressures and one is slightly more or else it wouldn't close.
-
01-01-2013, 10:49 PM #30
Professional Member*
- Join Date
- Nov 2001
- Location
- east kansas
- Posts
- 7,975
-
01-02-2013, 12:39 AM #31
Oh please. It's a vacuum switch. It closes when it senses a vacuum and opens when the inducer stops. There's nothing special about it. Its a temporary switch.. He didn't bypass it. The only thing it won't do is go into high fire if he didn't jumper the low and high fire wires.
The Lennox dual press switch is a joke to begin with. It's a switch. There's no need for four of them. It's open or closed.
A switch is a switch is a switch.
-
01-02-2013, 07:24 AM #32
Professional Member
- Join Date
- Jan 2007
- Location
- Mn the state where absolutey nothing is allowed
- Posts
- 1,097
so you dont know how to use a manometer either.
" a switch is a swith is a switch" huh, so are roll outs and limit switches. im guessing by that logic you'd be ok with just repacing any limit switch with one rated at 1000 deg... after all its just a switch.
great advice to a guy who came here to ask us how to proper;y troublshoot a p-sw.
iceman, you have enough posts for a pro membership here. apply and we can talk more in depth in the non-open forumsmy boss thinks its possible to repeal the laws of physics
-
01-02-2013, 12:15 PM #33
-
01-02-2013, 02:06 PM #34
Regular Guest
- Join Date
- Aug 2012
- Location
- Portland, Or
- Posts
- 45
ch4man
Maybe you should read my original post, and my follow up posts, I stated I installed a regular pressure switch that closes on vacum, and its running for now (temporarily) and came here to ask the question and I would be calling Lennox in the am about the original pressure switch problem Lennox had. Which I learned about here BTW, Thanks guys. I also stated Joe Blow ran the minimum vent and combustion air pipe and it wasnt operating correctly and I disconnected the combustion air pipe and added more air, so after I contact Lennox on switch and collector I will be going back to double check there venting on this sytem which Im sure ties into pressure switch issue. At no time did I say I was leaving switch. Maybe you try reading this whole thread before you start tripping
I appreciate all the 101 I got from everyone, and Im that much smarter. Thanks to all the helpful responses. Just ordered collector box and new pressure switch and will be returning to job to calculate the total vent piping. Thanks for the 101 everyone
-
01-02-2013, 02:09 PM #35
Regular Guest
- Join Date
- Aug 2012
- Location
- Portland, Or
- Posts
- 45
Thanks Chaard. Glad you actually read this thread lol. Appreciate your help
-
01-02-2013, 02:11 PM #36
Regular Guest
- Join Date
- Aug 2012
- Location
- Portland, Or
- Posts
- 45
Thanks to all the helpful responses everyone. Have a great New Year
-
01-02-2013, 06:48 PM #37
-
01-02-2013, 07:13 PM #38
-
01-02-2013, 07:47 PM #39
Professional Member
- Join Date
- Jan 2007
- Location
- Mn the state where absolutey nothing is allowed
- Posts
- 1,097
wow. was i that tough on you guys? need some thicker skin here.
ok lets go through together so i can also learn.
iceman, please be patient i really am trying to help. please post as many readings, model/serial numbers and anything that will help us help you.
how come i got beat up and he didnt?
.
i hope by now you realize the point of my rant is that at no time did you prove the switch was defective as opposed to doing its job. at no time did you prove it was running safe while you went to of all places the internet for help. do you have access to a combustion analyzer? are you a one man shop or are there any senior tech who can help guide you.
p.s. chaard yes a 1000 deg limit was a redicules analogy. but a pressure switch is still a safety switch. from what iceman wrote it was not the electrial part but the pressure sensing portion that was keeping the furnace from running in an ussafe condition.my boss thinks its possible to repeal the laws of physics


Reply With Quote