    Crank case heater

    On a Copland scroll usually has those hose clamp looking style crankcase heaters around the bottom portion area of the compressor, it has a constant 208/230 volts applied to it. I amped it out it's drawing no amps, I ohmed it out it was open, need to replace it, I amped out 3 others heaters same result, do they have some kind of ptcr piece in it, once it heats up to a certain temp, resistance increases doesn't allow power to flow through???? But then when ohming it out I should get a reading! Its a cch usually straight forward but being that I seen like 4 that were bad doesn't seem right,

  2. #2
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    5,135
    Post Likes
    I believe the most common type that I think you are describing get hot all of the time (not self regulating). They don't draw a lot of power, though. Usually it is less than an amp, if I remember correctly.

  3. #3
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    I know some run constantly and some have a temp controled shut off . Im not sure the means of witch they shut off i would cool them down and test them to make sure. Shouldnt take that long

  4. #4
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    Plz post back when you get to the bottom of this. Solid state relays that act similar to what your descriding come with ohm/temp charts. As well as cad cells. Im all ears

  5. #5
    Join Date
    Jun 2009
    Location
    DFW, TX
    Posts
    1,719
    Post Likes
    Did you check resistance and amp draw on the new heater? Because I once had a Fluke meter that wouldn't read ohms above a certain point, and I condemned all kinds of stuff before I figured it out... Amp draw will be so low you may not pick it up. I think the best test is to just see if its hot?

  6. #6
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    The ones I've seen draw between .5 and 1 amp. We must have changed 50 of them last spring/summer. I don't think they are incredibly reliable.

  7. #7
    Join Date
    Feb 2007
    Location
    Deep South
    Posts
    355
    Post Likes
    Most of those heaters I've seen about 70 watts (with comp # we can find out exactly) with 230V that wold be about 0.3 amps. Hard to read.

    To get more accurate reading you can loop wire five times in jaws of your amp meter then divide you reading by five for actual amps.

    Make sure heater is energized sometimes heater is locked out when comp running

  8. #8
    Join Date
    Sep 2010
    Location
    miami,fl.
    Posts
    2,253
    Post Likes
    Thread Starter
    i looked it up once i got home from work it is a 70 watt heater if you divide that by the incomming voltage 207 volts = .33 amps pretty much what you have stated. i emailed copeland tech support model and serial info but no response on any info. the heater did feel warm but with no amp draw nor any ohm reading was throwing me off. in this situation the heater runs continuous wired to the line side of contactor straight.

  9. #9
    Join Date
    Sep 2010
    Location
    miami,fl.
    Posts
    2,253
    Post Likes
    Thread Starter
    Quote Originally Posted by Core_d View Post
    Plz post back when you get to the bottom of this. Solid state relays that act similar to what your descriding come with ohm/temp charts. As well as cad cells. Im all ears
    i emailed copeland tech support but they never replied back with info. once i get an answer ill reply back. but for now ill say the heater is still good. it was warm not hot, has me iffy plus no ohms and no amps.............. maybe the amps were to low to pick up, but ill keep looking into this for future reference.

  10. #10
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    Thanks for the up date. After reading the posts ide say your meters not sensitive enough or more likley its heated its last case. If some cch did come with a thermistor type shut off someone would have posted it by now. Let me know

  11. #11
    Join Date
    Feb 2007
    Location
    Deep South
    Posts
    355
    Post Likes
    If you google copeland AE 4-1312 then go the list of CCH for described scroll comp.

    They are heater wire not solid state in this range size.

    You might be waiting a while for them to get back. Holidays and all

    If that is wrong size range comp shoot me back I have the data at office for all of them.
    Last edited by steve wright; 01-03-2013 at 11:05 PM. Reason: Addition info

  12. #12
    Join Date
    Jul 2011
    Location
    Lehigh Valley, PA
    Posts
    510
    Post Likes
    Using ohms law, if you have 208v (E) & .33amps (I), resistance (R) would be 630ohms. I wouldn't depend on a clamp on amp meter to accurately read .33amps but having said this, your clamp on may show something and if resistance is near 600ohms, it should be working. Watts = E*I, or in this case 68 watts

  13. #13
    Join Date
    Jan 2009
    Location
    IRELAND
    Posts
    55
    Post Likes
    I have come across this alot also.they seem to suffer on compressors with a sweatback to the suction with the water running down onto one spot on the heater

  14. #14
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    Quote Originally Posted by Capz View Post
    Using ohms law, if you have 208v (E) & .33amps (I), resistance (R) would be 630ohms. I wouldn't depend on a clamp on amp meter to accurately read .33amps but having said this, your clamp on may show something and if resistance is near 600ohms, it should be working. Watts = E*I, or in this case 68 watts
    Ohms law doesnt add up with alternating current. Not your basic triangle chart anyways lot of other factors peak voltage ect.
    Last edited by Core_d; 01-04-2013 at 07:53 PM. Reason: Misspell

  15. #15
    Join Date
    Feb 2007
    Location
    Deep South
    Posts
    355
    Post Likes
    It does for resistive loads the CCH is resistive.

    You are right that it will not work with capacitive or inductive loads.

  16. #16
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    Quote Originally Posted by steve wright View Post
    It does for resistive loads the CCH is resistive.

    You are right that it will not work with capacitive or inductive loads.
    Yea your right i just tested this with my oven😊 worked like a charm. I do remember messing with this in school with light bulbs and it wouldnt add up. I believe we came to the conclusion bulbs did not actually pull the wats they were rated for. Thanks for the correction

  17. #17
    Join Date
    Nov 2003
    Posts
    1,867
    Post Likes
    Quote Originally Posted by Core_d View Post
    Yea your right i just tested this with my oven�� worked like a charm. I do remember messing with this in school with light bulbs and it wouldnt add up. I believe we came to the conclusion bulbs did not actually pull the wats they were rated for. Thanks for the correction
    Incandescent bulbs are also resistive loads. They are heaters.

  18. #18
    Join Date
    Feb 2007
    Location
    Deep South
    Posts
    355
    Post Likes
    Hey I'm at 41 years and the only thing I know for sure is the more I learn the more there is to learn.

    In the field there are many things like instrument error that can make not add up.



    Keep going after it.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •