Page 2 of 2 FirstFirst 12
Results 14 to 18 of 18
  1. #14
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    4,605
    Post Likes
    Quote Originally Posted by Capz View Post
    Using ohms law, if you have 208v (E) & .33amps (I), resistance (R) would be 630ohms. I wouldn't depend on a clamp on amp meter to accurately read .33amps but having said this, your clamp on may show something and if resistance is near 600ohms, it should be working. Watts = E*I, or in this case 68 watts
    Ohms law doesnt add up with alternating current. Not your basic triangle chart anyways lot of other factors peak voltage ect.
    Last edited by Core_d; 01-04-2013 at 08:53 PM. Reason: Misspell

  2. #15
    Join Date
    Feb 2007
    Location
    Georgia
    Posts
    205
    Post Likes
    It does for resistive loads the CCH is resistive.

    You are right that it will not work with capacitive or inductive loads.

  3. #16
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    4,605
    Post Likes
    Quote Originally Posted by steve wright View Post
    It does for resistive loads the CCH is resistive.

    You are right that it will not work with capacitive or inductive loads.
    Yea your right i just tested this with my oven😊 worked like a charm. I do remember messing with this in school with light bulbs and it wouldnt add up. I believe we came to the conclusion bulbs did not actually pull the wats they were rated for. Thanks for the correction

  4. #17
    Join Date
    Nov 2003
    Posts
    1,867
    Post Likes
    Quote Originally Posted by Core_d View Post
    Yea your right i just tested this with my oven�� worked like a charm. I do remember messing with this in school with light bulbs and it wouldnt add up. I believe we came to the conclusion bulbs did not actually pull the wats they were rated for. Thanks for the correction
    Incandescent bulbs are also resistive loads. They are heaters.

  5. #18
    Join Date
    Feb 2007
    Location
    Georgia
    Posts
    205
    Post Likes
    Hey I'm at 41 years and the only thing I know for sure is the more I learn the more there is to learn.

    In the field there are many things like instrument error that can make not add up.



    Keep going after it.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.