Results 1 to 13 of 18
Thread: Crank case heater
12-31-2012, 11:24 PM #1
- Sep 2010
- miami,fl.
- 317
Crank case heater
On a Copland scroll usually has those hose clamp looking style crankcase heaters around the bottom portion area of the compressor, it has a constant 208/230 volts applied to it. I amped it out it's drawing no amps, I ohmed it out it was open, need to replace it, I amped out 3 others heaters same result, do they have some kind of ptcr piece in it, once it heats up to a certain temp, resistance increases doesn't allow power to flow through???? But then when ohming it out I should get a reading! Its a cch usually straight forward but being that I seen like 4 that were bad doesn't seem right,
12-31-2012, 11:52 PM #2
Professional Member*
- Apr 2003
- Maple Grove, MN
- 720
I believe the most common type that I think you are describing get hot all of the time (not self regulating). They don't draw a lot of power, though. Usually it is less than an amp, if I remember correctly.
12-31-2012, 11:52 PM #3
I know some run constantly and some have a temp controled shut off . Im not sure the means of witch they shut off i would cool them down and test them to make sure. Shouldnt take that long
01-01-2013, 12:33 AM #4
Plz post back when you get to the bottom of this. Solid state relays that act similar to what your descriding come with ohm/temp charts. As well as cad cells. Im all ears
01-01-2013, 11:03 PM #5
- Jun 2009
- Garland, TX
- 349
Did you check resistance and amp draw on the new heater? Because I once had a Fluke meter that wouldn't read ohms above a certain point, and I condemned all kinds of stuff before I figured it out...
Amp draw will be so low you may not pick it up. I think the best test is to just see if its hot?
01-02-2013, 07:42 AM #6
The ones I've seen draw between .5 and 1 amp. We must have changed 50 of them last spring/summer. I don't think they are incredibly reliable.
01-03-2013, 07:12 PM #7
- Feb 2007
- Georgia
- 116
Most of those heaters I've seen about 70 watts (with comp # we can find out exactly) with 230V that wold be about 0.3 amps. Hard to read.
To get more accurate reading you can loop wire five times in jaws of your amp meter then divide you reading by five for actual amps.
Make sure heater is energized sometimes heater is locked out when comp running
01-03-2013, 09:36 PM #8
- Sep 2010
- miami,fl.
- 317
i looked it up once i got home from work it is a 70 watt heater if you divide that by the incomming voltage 207 volts = .33 amps pretty much what you have stated. i emailed copeland tech support model and serial info but no response on any info. the heater did feel warm but with no amp draw nor any ohm reading was throwing me off. in this situation the heater runs continuous wired to the line side of contactor straight.
01-03-2013, 09:41 PM #9
- Sep 2010
- miami,fl.
- 317
i emailed copeland tech support but they never replied back with info. once i get an answer ill reply back. but for now ill say the heater is still good. it was warm not hot, has me iffy plus no ohms and no amps.............. maybe the amps were to low to pick up, but ill keep looking into this for future reference.
01-03-2013, 10:05 PM #10
Thanks for the up date. After reading the posts ide say your meters not sensitive enough or more likley its heated its last case. If some cch did come with a thermistor type shut off someone would have posted it by now. Let me know
01-03-2013, 11:04 PM #11
- Feb 2007
- Georgia
- 116
If you google copeland AE 4-1312 then go the list of CCH for described scroll comp.
They are heater wire not solid state in this range size.
You might be waiting a while for them to get back. Holidays and all
If that is wrong size range comp shoot me back I have the data at office for all of them.Last edited by steve wright; 01-03-2013 at 11:05 PM. Reason: Addition info
01-04-2013, 07:35 AM #12
- Jul 2011
- Lehigh Valley, PA
- 221
Using ohms law, if you have 208v (E) & .33amps (I), resistance (R) would be 630ohms. I wouldn't depend on a clamp on amp meter to accurately read .33amps but having said this, your clamp on may show something and if resistance is near 600ohms, it should be working. Watts = E*I, or in this case 68 watts
01-04-2013, 07:45 AM #13
- Jan 2009
- IRELAND
- 23
I have come across this alot also.they seem to suffer on compressors with a sweatback to the suction with the water running down onto one spot on the heater