Quote Originally Posted by Snapperhead View Post
But my original question was .... if you take off a 355k pilot valve , and replace it with a 160k , will it lower the gas flow to the main burner ?
Yes, a valve rated at less than half the capacity will not flow as much gas at a given inlet pressure. Very similar to putting too small of a gas flex on a unit. It will restrict the flow.