    Confused heater ignitor not glowing 13 V on gas valve only?

    Heater is not glowing, on Heat demand the blower comes on , you hear a initial click first but nothing past that point. Replaced the Honeywell Flame Rod Assembly as it was brittle and broke when checking it. Nothing. Tested the Pressure Switch (can) and it appears to be working correctly. Check voltage to gas valve and only read 13 volts when the unit is ON demand. My other unit will read at 24 volts at this point. I do not see any broken wires. What else can I check?

  2. #2
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    Call a tech this isn't a DIY site read the rules.

  3. #3
    Join Date
    May 2011
    Location
    Central Texas
    Posts
    101
    Post Likes
    I'm sorry bud, but this isn't a DIY section. If your in the trade you can apply for pro membership and this can be discussed in the pro section. If you aren't in the trade you need to call a pro out.