Semi-hermetic valves leaking?
Saw a compressor short cycling twice a second. Found the low pressure control out of calibration, made it work, though i think it should be replaced.
While setting the low pressure control (with my gauge on), i notice the pressure climbing from 10psig, to the 30psig in about 10 seconds.
Is this the soldenoid valve or the compressor valves? if it's the compressor valves, how do i know if it's suction or discharge valves? (though i recognize that both should be replaced during a rebuild)
-
Easiest way to diagnose this one would be to take a look at that solenoid valve. It'll be cold on the outlet if it's leaking through that bad.
I never bother trying to figure out ahead of time if its bad suction or bad discharge valves. If it's got bad valves, I'm going to be replacing the valve plate either way.
-
 Originally Posted by wdshea
Saw a compressor short cycling twice a second. Found the low pressure control out of calibration, made it work, though i think it should be replaced.
While setting the low pressure control (with my gauge on), i notice the pressure climbing from 10psig, to the 30psig in about 10 seconds.
Is this the soldenoid valve or the compressor valves? if it's the compressor valves, how do i know if it's suction or discharge valves? (though i recognize that both should be replaced during a rebuild)
sounds like its low refrigerant, or restriction and the compressor is cycling off due to the low pressure control setting. once the pressure rises to what ever the cut in setting/ high event is set to then the compressor will kick back on. does the pressures go from 10 psig up to 30 psig while its still running. or does the compressor shut off then the pressure rises up to 30psig??? more info would be good. did you get it going?
-
turn off high side service valve while running , and when your low side drops to 5 psi , quickly turn off the power to compressor.
This simulates the LL valve closing . If you see the suction begin to rise 10 - 30 like its been doing , then your valves are shot
-
I think what snapperhead meant was to shut off the liquid reciever valve to simulate the lls closing never shut off the high side on compressor when its runing very bad idea
Honeywell you can buy better but you cant pay  more
I told my wife when i die to sell my fishing stuff for what its worth not what i told her i paid for it
-
What was the reason for you being there? Was there a problem or was this something you noticed? Low charge, llsv leaking by, long line set is me just thinking out loud.
-
i was working on a line cooler that is in the same rack. there are about 10 refrigeration circuits on the rack.
thanks for the service valve trick, i feel like a dumbass for not thinking of that myself.
anthony, the compressor would pump down to 10psig (it was struggling to get from ~13 to 10 psig), then after the comp was off the pressure would slide back up to 30 and do it again. that would take ~10 seconds.
-
yep , struggling to pump down is another sign the valves are leaking
-
 Originally Posted by Snapperhead
yep , struggling to pump down is another sign the valves are leaking
^^^^^^
-
Are you only watching it do this once or twice, or does it continue to do this on and on? Sometimes with long lineset or large evaps, it can take a couple of pumpdowns before the low side is clear of liquid refrigerant.
-
 Originally Posted by crazzycajun
I think what snapperhead meant was to shut off the liquid reciever valve to simulate the lls closing never shut off the high side on compressor when its runing very bad idea
Yes sir. You close the discharge service valve and start it the valves will difinately get junked. Just close the suction service valve. If it pull down comp valves good go to LLS. If it doesn't pull down and hold get a valve plate.
-
 Originally Posted by MicahWes
Are you only watching it do this once or twice, or does it continue to do this on and on? Sometimes with long lineset or large evaps, it can take a couple of pumpdowns before the low side is clear of liquid refrigerant.
This
Officially, Down for the count
YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET
I know enough to know, I don't know enough
Liberalism-Ideas so good they mandate them
-
While you have that valve plate off you want to check piston and bore for wear and damage, if it is air cooled (no oil pump) you will need to check the wrist pin too.
When you drop a suction valve lots of time other damage will happen