    Boiler question/ can't remember operation

    Been a while since I serviced a small residential boiler. It is a Weil Mclain gv-5 series. Has one baseboard fin tube zone, and a a/h with a water coil in it with its own cir pump for forced air heat. Heres what I can't remember, when there is a call from the stat. The system pump is supposed to start. The system pump is being used as the cir for the baseboard zone. There is a dayton indoor/outdoor aquastat in the low voltage circuit from the stat. The only time the pump does run if I put a call from the a/h. I think there is something wrong with the aquastat controller, but the pump stills gets power from the boiler control board. I have seen voltage on the terminals on the auquastat. Someone please refresh my memory, or kick my if I completely missed the mark here

  2. #2
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    5,104
    Quote Originally Posted by Oldsolarguy View Post
    Been a while since I serviced a small residential boiler. It is a Weil Mclain gv-5 series. Has one baseboard fin tube zone, and a a/h with a water coil in it with its own cir pump for forced air heat. Heres what I can't remember, when there is a call from the stat. The system pump is supposed to start. The system pump is being used as the cir for the baseboard zone. There is a dayton indoor/outdoor aquastat in the low voltage circuit from the stat. The only time the pump does run if I put a call from the a/h. I think there is something wrong with the aquastat controller, but the pump stills gets power from the boiler control board. I have seen voltage on the terminals on the auquastat. Someone please refresh my memory, or kick my if I completely missed the mark here
    If you have 2 zones, it'd be best to have each one seperated with it's own pump/zone valves. Especially when you get into dramatically different forms of radiation.

    If not, and your using one pump, then you need to set it so the single pump runs off of 1 thermostat.
    If your not seperated, and your trying to use 2 stats to turn on one pump, your going to overheat one of the areas.
    UNLESS, the air handler is oversized. Then although the coil gets hot, the air wouldn't blow across the coil and heat the area when it's satisfied.

    How it's wired is going to determine how it operates. To many ways to do it without being there though.
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

  3. #3
    Join Date
    Feb 2007
    Location
    Fremont, Indiana
    Posts
    1,646
    Continuous pump with bypass loop and zone valves. Stats wired to valves in each zone.

    sent from my Samsung Galaxy Note
    Member of the "Work Exchange Program"
    "Will work for knowledge"

    "Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
    A Einstein

  4. #4
    Join Date
    Jan 2013
    Location
    Henry county,ky
    Posts
    82
    Here's some better info of the setup. The boiler cir is being used as the primary cir for the baseboard heat. No zone valves, just pumps. I just don't understand how the system worked when the primary cir only runs with the burners running. The aqua stat being used is a 2 bulb differential control measuring outdoor air and the water temp to ramp up and down the water temp according to the outdoor temp. The boiler is on its own stat, which is broke thru the aqua stat. The air handlers have thier own dedicated stats. I have already suggested to get rid of the aqua stat and turn the high limit down to 150. Wire the stat direct to the low voltage terminals on the boiler and let the burners ride against the high limit while the pump will cir whenever the stat calls, with or without the burners. The customer is upset at the fact of replacing the aqua stat with something that is designed to work the way I have described above due to cost. Any other thoughts on this fellows?

  5. #5
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,367
    Sounds like the ODR aquastat was wired in wrong. Should only be wired into the burner LV control circuit.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?