Results 27 to 31 of 31
Thread: annoying compressor problem
-
01-03-2013, 05:59 PM #27
Professional Member
- Join Date
- Feb 2007
- Location
- Georgia
- Posts
- 116
If that comp had mineral oil and you put r401 without changing to alky oil I bet comp seizing up.
As a last ditch effort you might try some Supco 88, sometimes it works sometimes not.
-
01-03-2013, 09:36 PM #28
Professional Member
- Join Date
- Aug 2007
- Location
- Illinois
- Posts
- 90
I would say oil logged or the oil got washed out of the compressor. I use 409 for 12 systems and have zero problems.
-
01-03-2013, 11:16 PM #29
Professional Member
- Join Date
- Feb 2007
- Location
- Georgia
- Posts
- 116
Yea I agree.
Sometimes you can add a little AB lubricant and it will help bring oil back
-
01-04-2013, 08:06 AM #30
Regular Guest
- Join Date
- Jan 2009
- Location
- IRELAND
- Posts
- 23
Sounds like its possibly been overcharged .I would ignore sight glass and charge system measuring subcooling off condenser and superheat off cooling coil
-
01-17-2013, 04:42 PM #31
Curious if you resolved the problem...


Reply With Quote