combustion analyzer testing
So I use a combustion analyzer to determine cracks in heat exchanger and other tests. The people I work with and talked to other service techs and no one in my area uses them. I am thinking your crazy for not using one. Oh well one up for me I guess.
-
12-30-2012, 01:10 PM #2
Good job. Now start using it to properly tune any appliance you touch.
A good class to take is @ NCI by Jim Davis.
www.nationalcomfortinstitute.com
-
12-30-2012, 01:13 PM #3
I wish mine would get sent back already, I thought you died gravity, been gone awhile lol!
-
12-30-2012, 04:30 PM #4
Does anyone regularly check their combustion analyzers with calibration gas? I just pegged my analyzer when I looked away to answer customer on blower motor change. Found bad regulator in gas valve causing over firing. Just ordered calibration gas and will now check it often.
-
12-31-2012, 11:26 AM #5
Professional Member
- Join Date
- Mar 2010
- Location
- Rochester, NY
- Posts
- 257
I was doing 2 c&c on 2 furnaces a couple of weeks ago, both goodman furnaces. I found cracked hx on both furnaces (visual) so I fired up my 327 to see how they were operating. Furnace #1 had rising CO so I shut it down and disabled it. Furnace #2 had stable CO under 60ppm so I left it in operation and advised the customer that both HX needed to be replaced. I would not have know the difference without my CA as they both looked the same as far as flame apperance.
-
12-31-2012, 02:35 PM #6
Didn't red tag it?
-
12-31-2012, 06:33 PM #7
-
12-31-2012, 06:43 PM #8
Professional Member*
- Join Date
- Sep 2005
- Location
- North GA
- Posts
- 17,279
GA-HVAC-Tech
Galatians 2:20-21; Colossians 1: 21-22 & 26-27; 3:1-4; Romans Ch's 5-6-7-8
2 Chronicles 7:14
Quality work at a fair price with excellent customer service.
-
01-01-2013, 07:11 AM #9
-
01-01-2013, 09:39 AM #10
Professional Member
- Join Date
- Mar 2010
- Location
- Rochester, NY
- Posts
- 257
This is a special situation where my mother ownes an appartment building so if I tell them the furnace needs repair they will authorize the repair. I have two new HX on the truck but have not been able to do the work yet due to a back injury. Also if the second furnace was unstable or if it had high CO i would have disabled it also. These are goodman 80% not that it matters much a cracked hx is a cracked hx.
-
01-01-2013, 09:49 AM #11
Professional Member*
- Join Date
- Sep 2005
- Location
- North GA
- Posts
- 17,279
I would be VERY careful with bending safety requirements on bad HXE's... one could cause something they do not want on their conscious for the rest of their lives... like a CO poisoning issue.
Having said that: A combustion analyzer will tell a lot more than a visual inspection. This one is a tuff call.
Personally, I think I would have provided a few elec space heaters and tagged it.GA-HVAC-Tech