    Quote Originally Posted by NY2GA01 View Post
    but this was a heat pump, so the use of a one way filter is like having no filter at all.

    Still not a 100% on if it killed the compressor.
    Well, it'll definetly filter in the cool mode. I'm not sure if the moisture or contaminants gets pushed back out of the dryer during the heat cycle or the refrigerant simply flows around the core!! Maybe Andy Schoen or somebody could explain?

  2. #15
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,596
    What's the numbers look like when you fired it up? I was curious if the desiccant left the drier and stopped up something.

  3. #16
    Join Date
    Aug 2004
    Posts
    20
    Let me guess. It's a Sporlan too? I noticed the diaper they have put on the outlet side of the new ones to beat the ALCO demo that showed them releasing the crud caught around the ends when the pressure backed off?
    Now that they have been bought maybe their parent company will replace them with theirs. P/H has great filter/driers.

  4. #17
    Join Date
    Jan 2011
    Location
    Metro Atlanta
    Posts
    790
    Quote Originally Posted by ryan1088 View Post
    What's the numbers look like when you fired it up? I was curious if the desiccant left the drier and stopped up something.
    I suspect the expansion valve to be stopped up. I have to go back to the job and figure out if I can figure out how to get the pressure correct, my pressures were all messed up in both heating or cooling mode.

    This is a business that is open M-F only, and on Friday's they leave at 4 pm sharp:.
    Last edited by NY2GA01; 12-31-2012 at 12:04 AM.
    The opinions expressed by me are not that of my employer.


    insulation modern marvels
    http://www.youtube.com/watch?v=g37riSkyZzM

  5. #18
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,596
    Sounds like more pictures are in order when you take the expansion valve loose and see little desiccant balls!!

  6. #19
    Join Date
    Jun 2012
    Location
    Northern NV
    Posts
    155
    A bi-flow filter dryer is actually TWO filter dryers in one can with back flow valves to ensure that the crud caught does not get washed back into the system when reversing flow. Whack one up and take a look...

  7. #20
    Join Date
    Jul 2011
    Location
    Lehigh Valley, PA
    Posts
    471
    I had a S-163 hooked to my Ducane heatpump from 2002 to 2012. Guess what...The Ducane still works. Never had a single issue in the summer with cooling. I removed it last spring for the hell of it, knew it wasn't right for the heat mode. Now let me say, I don't use the heatpump for heat all that often since I am able to heat with coal. But the Ducane still works well. Has a scroll in case you were wondering.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event