Results 14 to 20 of 20
Thread: Found this on a heat pump
-
12-30-2012, 05:51 PM #14
-
12-30-2012, 05:56 PM #15
What's the numbers look like when you fired it up? I was curious if the desiccant left the drier and stopped up something.
-
12-30-2012, 06:39 PM #16
Regular Guest
- Join Date
- Aug 2004
- Posts
- 17
Let me guess. It's a Sporlan too? I noticed the diaper they have put on the outlet side of the new ones to beat the ALCO demo that showed them releasing the crud caught around the ends when the pressure backed off?
Now that they have been bought maybe their parent company will replace them with theirs. P/H has great filter/driers.
-
12-30-2012, 10:41 PM #17
I suspect the expansion valve to be stopped up. I have to go back to the job and figure out if I can figure out how to get the pressure correct, my pressures were all messed up in both heating or cooling mode.
This is a business that is open M-F only, and on Friday's they leave at 4 pm sharp:.Last edited by NY2GA01; 12-30-2012 at 11:04 PM.
The opinions expressed by me are not that of my employer.

-
12-30-2012, 10:50 PM #18
Sounds like more pictures are in order when you take the expansion valve loose and see little desiccant balls!!
-
01-08-2013, 07:47 PM #19
Professional Member
- Join Date
- Jun 2012
- Location
- Northern NV
- Posts
- 101
A bi-flow filter dryer is actually TWO filter dryers in one can with back flow valves to ensure that the crud caught does not get washed back into the system when reversing flow. Whack one up and take a look...
-
01-08-2013, 08:24 PM #20
Professional Member
- Join Date
- Jul 2011
- Location
- Lehigh Valley, PA
- Posts
- 226
I had a S-163 hooked to my Ducane heatpump from 2002 to 2012. Guess what...The Ducane still works. Never had a single issue in the summer with cooling. I removed it last spring for the hell of it, knew it wasn't right for the heat mode. Now let me say, I don't use the heatpump for heat all that often since I am able to heat with coal. But the Ducane still works well. Has a scroll in case you were wondering.



Reply With Quote