Trane makes 3 hard start kits which comprise of a cap and a potential relay..
BAYKSKT257,258,259,260
My scroll compressor unit calls for a 260 but the supplier gave me a 257. Claims this will work but I'm not so sure about this one. I believe the cap is OK but wouldnt the potential relay have a different voltage setting (pickup and dropout) for a scroll compressor? Any help would be appreciated.
-
12-05-2006, 10:52 AM #2
Professional Member
- Join Date
- Aug 2006
- Posts
- 26
hard start on a scroll? i thought you only use them on recip's with a TXV
-
12-05-2006, 12:44 PM #3
The 60 is used for scrolls when you get light dimming on startup. That is the primary reason for using a hard start kit on scrolls. I haven't heard of using the 57 on them but scrolls so seldom need a start kit that we've had a 60 when needed.
Never knock on Death's door. Ring the bell and run, he hates that.
Views expressed here are my own and not neccessarily those of any company I am affiliated with.
-
12-05-2006, 01:06 PM #4
No return.
- Join Date
- Jul 2006
- Location
- NW burbs of Detroit
- Posts
- 6,058
Some mfgs call for them in larger tonnage when loading is an issue.
-
12-11-2006, 04:55 PM #5
Regular Guest
- Join Date
- Jun 2006
- Posts
- 111
Specifications for the models you referenced:
BAYKSKT257: 135mfd x 330 cap, relay 35amp coil, 239volt pick up, 135volt dropout on relay
BAYKSKT258: same cap, 35amp coil, 223v pick up, 152v dropout on relay
BAYKSKT259: same cap, 35amp coil, 204v pick up, 150v dropout on relay
BAYKSKT260: same cap, 50amp coil, 153v pick up, 115v dropout on relay