Page 1 of 2 12 LastLast
Results 1 to 13 of 15
  1. #1
    Join Date
    Oct 2005
    Location
    Louisiana
    Posts
    1

    Lennox Package Unit Model# TGA120S2BH1Y (Gas Heat) NO HEAT

    My partner went on a service call for this unit because the heat wouldn't come on. It has 2 boards on it and the board with the indicator light is blinking 3 times. On the unit, it says that if the light is blinking 3 times is is usually flame overthrow but he checked it and it checked out ok. He has ordered a new board but we are hoping someone has info or troubleshooting advice on this unit. We're not too familiar with Lennox units.

  2. #2
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,745
    What is flame overthrow?
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

  3. #3
    Join Date
    Oct 2012
    Location
    La Crosse, WI
    Posts
    256
    I think it is rollout. Does that have the manual-reset rollout in it. Where the terminals corroded and not making a good connection?

  4. #4
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,745
    If that's the case, there is much more that needs to be checked
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

  5. #5
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,133
    flame what...... never heard of the term in all my life..... good luck .......
    it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair

  6. #6
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,745
    Quote Originally Posted by carmon View Post
    flame what...... never heard of the term in all my life..... good luck .......

    Overthrow
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

  7. #7
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,133
    oh now I get it .....
    it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair

  8. #8
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    3,605
    Quote Originally Posted by starkey View Post
    It has 2 boards on it and the board with the indicator light is blinking 3 times. On the unit, it says that if the light is blinking 3 times is is usually flame overthrow but he checked it and it checked out ok.
    The 3 flash code - Flame Rollout Switch Open or Prove Switch Open or Closed.

    The Flame Rollout is a 290ºf (+/- 12ºf ), manual reset switch.

    The Combustion Air Prove Switch closes on negative pressure fall, showing the inducer motor is up to speed before allowing the ignition sequence to continue.

    Did you have the door/panel back on burner compartment when you were testing?

    Did you do any testing of the combustion blower or it's capacitor?

    Sorry, but I don't post manuals in this "OPEN" forum.
    Instead of learning the tricks of the trade, learn the trade.

  9. #9
    Join Date
    Feb 2007
    Location
    Central NJ
    Posts
    366
    I always check the circuit path from the molex plug connection(s), just because the roll out is closed doesn't mean it's finishing

  10. #10
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    14,474
    We don't discuss step by step diagnostics in the open forums. Get your post count up to 15 and apply for pro membership, so we can deal with your questions in the restricted access Pro forums.

    Even the T series has a wiring diagram. I would follow it and everything should be clear. What is the serial number?

  11. #11
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,218
    hell, he's a one & done, apparently didn't get the answer they wanted.

    and I'm a little concerned about the "partner" thing?????
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  12. #12
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    14,474
    Quote Originally Posted by dandyme View Post
    and I'm a little concerned about the "partner" thing?????
    I don't think Louisiana is one of "those" states...

  13. #13
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,745
    Quote Originally Posted by timebuilder View Post
    I don't think Louisiana is one of "those" states...
    In Loozy they call them "Pardners"
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

Page 1 of 2 12 LastLast