01-07-2013, 07:40 PM #27
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
[QUOTE=Navy06;14937321 you will always need a defrost on any system.[/QUOTE]
-
01-08-2013, 12:14 PM #28
-
01-08-2013, 06:21 PM #29
Professional Member*
- Join Date
- Oct 2009
- Location
- Raleigh, NC
- Posts
- 435
I have seen maybe 5 (standard TXV style) walk-ins with sensing elements in the coil in maybe nearly 1000 walk-ins. WHY are sensing elements in the coil more reliable with better control? Why don't all the WIC manufacturers use this system of control if it is hands down superior? Cost certainly isn't the concern.
-
01-08-2013, 06:56 PM #30
In 90% of WICs it's not nessisary nor is a defrost timer. But 10% of them will be let's say special. Prone to frosting up for non refrigeration system issues. The bulb in coil is a more effective way to control this frosting because it will shut comp off at the onset and start comp as soon as coil reaches cut in temp,too warm for frost to exist. Where as a timer is all about timed cycles. Prop door open 10 minuts after a defrost cycle on a humid day and a service call and manual defrost are likely.
-
01-08-2013, 07:49 PM #31
Professional Member
- Join Date
- Jul 2011
- Location
- Lehigh Valley, PA
- Posts
- 225
T-stat bulbs in coils function just as a refer unit using a Ranco low pressure control switch for temperature control as you might see on smaller/older reach-in's. I've experimented with either/or on 10' pizza make tables and the large retarders and compared watching suction temps. It's kind of neat and a good study in refrigeration theory.