Page 1 of 3 123 LastLast
Results 1 to 13 of 31
  1. #1
    Join Date
    Feb 2012
    Location
    Louisiana
    Posts
    66

    Walk in cooler without defrost

    I went on my first solo refrigeration service call today and it was stuck in defrost. I turned the wheel until it finally clicked on, took out the timer screws and let it run. Called boss and told him what was up and he said to just let it run without defrost until we get to it next week (probably not until Wednesday). I'm sure I should have gone and gotten a new defrost timer and put it in, but I'm still just a noob doing what I'm told. Is it OK to leave it running without defrost for 5 days?

  2. #2
    Join Date
    Mar 2008
    Location
    kansas
    Posts
    103
    What was the t stat set to, was it a beer box is the box in decent shape (door seals etc).Now the varibles you cant control do the store idiots leave door open go in and out 3000 times an hour. But just for refernce a lot of 35f-40f wi dont have defrost clocks
    Honeywell you can buy better but you cant pay more

    I told my wife when i die to sell my fishing stuff for what its worth not what i told her i paid for it

  3. #3
    Join Date
    Feb 2012
    Location
    Louisiana
    Posts
    66
    Stat set to 35. It is actually a walk in cooler in a restaurant that has a small walk in freezer inside of it...seems to be in fairly good shape. Crazy, are you a wayward cajun that found your way to Kansas?

  4. #4
    Join Date
    May 2009
    Location
    northern kentucky
    Posts
    137
    If it is a cooler it should not need defrost.

  5. #5
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    2,301
    Now you have what's called off cycle defrost. As long as you don't have leaking doors, open doors, or an excessive load this time of year you should be fine. I like to have timers on my bigger boxes .

  6. #6
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,738
    Quote Originally Posted by cajunhvac75 View Post
    Is it OK to leave it running without defrost for 5 days?
    Worst thing that will happen is the coil will freeze. In my experience, clocks are a necessity on keg coolers and chicken coolers. The problem with many restaurants is the employees prop doors open. There are a number of other factors, that are less relevant. Many manufacturers have begun putting defrost clocks in their condensing units because they have realized the issues. A properly set HW or WR mechanical temp control with the sensing bulb inserted in the coil will accomplish the off cycle defrost with no possibility of freezing, providing the system is set up and charged properly.
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

  7. #7
    Join Date
    Aug 2010
    Location
    Garland, TX
    Posts
    39
    Stick a tstat of a walk in cooler in the coil? What? You should never do that! Return air is where the bulb should be at, t-stat set to cut out at 32 degres in ice water(calibrate). The numbers don't always match up. Super heat at 10-12 degrees with 4 x 30min defrost. The lowee cutout will ensure proper food temp coming out of the w/i/c. These defrost are needed in the south, with the warner air and high humidity situations. This is an off cycle defrost. You should be good, but if they call back with a warm box. Take the timer and be done with the call.

  8. #8
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    2,190
    Quote Originally Posted by J_Bridge View Post
    Stick a tstat of a walk in cooler in the coil? What? You should never do that! Return air is where the bulb should be at.
    depends on the stat you choose. There are 2 types of bulbs , one needs to be on coil , one hanging in air.

  9. #9
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    14,468
    The problem with merely sensing air temp when using off-cycle defrost is that the air can be warm enough to keep the compressor running, while the coil is already frosted, making the frosting worse, and unable to cool the air. When you have the sensing part embedded in the evap coil, you will trigger the compressor to cycle off, clearing the frost, and then when it comes back on, you are actually getting the air-cooling job done. In the case of using an air temperature thermostat, you MUST have a timer to force a defrost once in a while, for the reason I gave, above.

  10. #10
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,738
    Quote Originally Posted by J_Bridge View Post
    Stick a tstat of a walk in cooler in the coil? What? You should never do that! .
    Why not?
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

  11. #11
    Join Date
    Aug 2002
    Location
    Orange County CA
    Posts
    1,084
    Low pressure controls save lives....Compressor lives

    You can get by in setting the Low Pressure control to a higher cut in temp. If you "cut in" at 38*- 40* (converted coil temp estimated) and "cut out" at 18*- 20* (converted coil temp estimated), you'd be surprised how long and how well it will run like that. The warmer "cut in" will defrost it every time it off cycles. Not to mention , you can mellow out comp cycle starts at the same time. You have to play with the numbers , but it works almost all the time.
    The pressure control will run a system (if set up correctly), better than a t-stat most of the time.

    Most knuckleheads bury a Med Temp system LP control to cut out at 3-5 #. Every time it pumps down, you drag the coil temp into the toilet. There is no need for that.

  12. #12
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    2,301
    Quote Originally Posted by NedFlanders View Post
    Low pressure controls save lives....Compressor lives

    You can get by in setting the Low Pressure control to a higher cut in temp. If you "cut in" at 38*- 40* (converted coil temp estimated) and "cut out" at 18*- 20* (converted coil temp estimated), you'd be surprised how long and how well it will run like that. The warmer "cut in" will defrost it every time it off cycles. Not to mention , you can mellow out comp cycle starts at the same time. You have to play with the numbers , but it works almost all the time.
    The pressure control will run a system (if set up correctly), better than a t-stat most of the time.

    Most knuckleheads bury a Med Temp system LP control to cut out at 3-5 #. Every time it pumps down, you drag the coil temp into the toilet. There is no need for that.
    This would work on a non pumpdown system. Otherwise you'll short cycle the compressor and be in worse shape than a frozen coil. I still have 3 coolers that operate this way and haven't had any trouble with them in the 3 years I've been doing refer work here.

  13. #13
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,738
    Quote Originally Posted by NedFlanders View Post
    Low pressure controls save lives....Compressor lives

    You can get by in setting the Low Pressure control to a higher cut in temp. If you "cut in" at 38*- 40* (converted coil temp estimated) and "cut out" at 18*- 20* (converted coil temp estimated), you'd be surprised how long and how well it will run like that. The warmer "cut in" will defrost it every time it off cycles. Not to mention , you can mellow out comp cycle starts at the same time. You have to play with the numbers , but it works almost all the time.
    The pressure control will run a system (if set up correctly), better than a t-stat most of the time.

    Most knuckleheads bury a Med Temp system LP control to cut out at 3-5 #. Every time it pumps down, you drag the coil temp into the toilet. There is no need for that.
    That may work in California, but it does not work where low ambient temps exist. If the outdoor temp is lower than the space temp, the refrigerant will stay in the receiver unless the receiver is wrapped in heat tape and insulated. This used to be a regular practice with R12
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •