    Nice work.
    But I must say I hate to see all that exposed copper mounted on un insulated masonry. (unless its insulated on the outside)

    95% system mounted on a giant heatsink = ?%.
    "The only way in which a human being can make some approach to knowing the whole of a subject is by hearing what can be said about it by persons of every variety of opinion and studying all modes in which it it can be looked at by every character of mind.
    No wise man ever acquired his wisdom in any mode but this."
    John Stuart Mill

  2. #15
    Join Date
    Feb 2006
    Posts
    509
    Quote Originally Posted by Wheelbaron View Post
    looks nice
    clean
    Thanks

    Quote Originally Posted by jlanesey View Post
    That's a lot of gas man! How do they split up the gas bill?

    Install looks nice and clean though.

    Would have taken the five minutes to paint the board though.
    The heat is included in the rent, this building is really old and there is really no easy way to split up heating. As for the paint, I'll be posting more boiler pics in the future and we got a good one going in soon. Thanks

    Quote Originally Posted by chuckcrj View Post
    Nice clean boiler work!

    Could have saved a pump by just using the buffer tank as your hydraulic seperation. I know, the low loss header comes with the boiler, which is why it always gets used.
    That's an awesome point Charles! I suppose we would just have to fit in the pump and piping for the domestic but that would work. It does seem rather redundant now to have two points of hydraulic separation.

  3. #16
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    I think you have 1 to many spirovents also, the buffer tank has one.

  4. #17
    Join Date
    Feb 2006
    Posts
    509
    Quote Originally Posted by Joehvac25 View Post
    They want check valve right at tank, all four ports so no gravity flow.
    Interesting, I'll have to look that up. Like Charles had mentioned.... it should be taken care of at the zone valves.

    Quote Originally Posted by rich pickering View Post
    Couldn't afford a coat of paint on the plywood?

    A boiler drain between the ball valve and the x-tank would be nice for service.
    I actually saw a drain like that on another boiler and thought it was a great idea.

    Quote Originally Posted by jnsrose View Post
    Do the install guys know you are putting up pictures of there work?
    No they don't.

    I put this up on the wall of pride cause I'm happy with their work. I'm not sure what your thoughts are but I have no bad intentions in this posting.

  5. #18
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Hot water can flow out of the supply or return, also boiler side could gravity flow through boiler.

  6. #19
    Join Date
    Feb 2010
    Location
    In a boiler room
    Posts
    7,049
    Quote Originally Posted by Joehvac25 View Post
    Hot water can flow out of the supply or return, also boiler side could gravity flow through boiler.
    There already is a check valve in the boiler pump, besides a little gravity flow through the boiler is a non-problem anyways.

    The boiler buddy should never be maintained at a certain temp, it is just buffer. The boiler only needs to fire when a zone is calling. Buffer tanks are ONLY necessary when the heat loss of the smallest zone is less than the lowest firing rate of the boiler.

    Example; If the boiler modulated down to 15,000 btu and the smallest zone has a heat loss of 16,000 btu's, a buffer tank is a waste of money.

  7. #20
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Quote Originally Posted by chuckcrj View Post
    There already is a check valve in the boiler pump, besides a little gravity flow through the boiler is a non-problem anyways.

    The boiler buddy should never be maintained at a certain temp, it is just buffer. The boiler only needs to fire when a zone is calling. Buffer tanks are ONLY necessary when the heat loss of the smallest zone is less than the lowest firing rate of the boiler.

    Example; If the boiler modulated down to 15,000 btu and the smallest zone has a heat loss of 16,000 btu's, a buffer tank is a waste of money.
    What I meant was on call for heat to the tank is maintained at a certain temp, not without a call for heat. I think I'm starting to split hairs here and I'm sure there won't be any or enuf gravity to make a difference it's just how it shows to install them in their manual.

  8. #21
    Join Date
    Aug 2011
    Location
    Denver PA
    Posts
    34
    Are u going to insulate?

  9. #22
    Join Date
    Feb 2006
    Posts
    509
    Quote Originally Posted by tlj000 View Post
    Nice work.
    But I must say I hate to see all that exposed copper mounted on un insulated masonry. (unless its insulated on the outside)

    95% system mounted on a giant heatsink = ?%.
    the board is mounted to an interior wall. there were no plans to insulate. i agree, it's a lot of copper but you have to realize too that this is a really old building downtown and there is no insulation in the walls. honestly, when comparing to the previous system, this new system will save the building owner tons.

  10. #23
    Join Date
    Aug 2008
    Location
    levittown, pa
    Posts
    64
    I do not like ball valves on expansion tanks, but thats me. Very nice work though! I get laughed at for painting floor heat manifolds red and blue.

  11. #24
    Join Date
    Sep 2012
    Location
    thomaston, ct
    Posts
    291
    Also no condensate drain on the exhaust close to boiler


    Sent from my iPhone using Tapatalk

  12. #25
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Quote Originally Posted by 4dblnkldude View Post
    I do not like ball valves on expansion tanks, but thats me. Very nice work though! I get laughed at for painting floor heat manifolds red and blue.
    You like to drain half the system with the tank and have to fug around with air in the system?

  13. #26
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Quote Originally Posted by Joehvac25 View Post
    What I meant was on call for heat to the tank is maintained at a certain temp, not without a call for heat. I think I'm starting to split hairs here and I'm sure there won't be any or enuf gravity to make a difference it's just how it shows to install them in their manual.
    Hey chuck reading this months later I can barely understand what I said, let alone expect you too lol.

    The buffer tank is only heated when there is a call for heat.

Page 2 of 3 FirstFirst 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event