Nice work.
But I must say I hate to see all that exposed copper mounted on un insulated masonry. (unless its insulated on the outside)
95% system mounted on a giant heatsink = ?%."The only way in which a human being can make some approach to knowing the whole of a subject is by hearing what can be said about it by persons of every variety of opinion and studying all modes in which it it can be looked at by every character of mind.
No wise man ever acquired his wisdom in any mode but this."
John Stuart Mill
-
01-01-2013, 10:29 AM #15
Professional Member
- Join Date
- Feb 2006
- Posts
- 507
Thanks
The heat is included in the rent, this building is really old and there is really no easy way to split up heating. As for the paint, I'll be posting more boiler pics in the future and we got a good one going in soon. Thanks
That's an awesome point Charles! I suppose we would just have to fit in the pump and piping for the domestic but that would work. It does seem rather redundant now to have two points of hydraulic separation.
-
01-01-2013, 10:44 AM #16
I think you have 1 to many spirovents also, the buffer tank has one.
-
01-01-2013, 03:06 PM #17
Professional Member
- Join Date
- Feb 2006
- Posts
- 507
Interesting, I'll have to look that up. Like Charles had mentioned.... it should be taken care of at the zone valves.
I actually saw a drain like that on another boiler and thought it was a great idea.
No they don't.
I put this up on the wall of pride cause I'm happy with their work. I'm not sure what your thoughts are but I have no bad intentions in this posting.
-
01-01-2013, 03:16 PM #18
Hot water can flow out of the supply or return, also boiler side could gravity flow through boiler.
-
01-02-2013, 12:00 AM #19
There already is a check valve in the boiler pump, besides a little gravity flow through the boiler is a non-problem anyways.
The boiler buddy should never be maintained at a certain temp, it is just buffer. The boiler only needs to fire when a zone is calling. Buffer tanks are ONLY necessary when the heat loss of the smallest zone is less than the lowest firing rate of the boiler.
Example; If the boiler modulated down to 15,000 btu and the smallest zone has a heat loss of 16,000 btu's, a buffer tank is a waste of money.
-
01-02-2013, 07:42 AM #20
What I meant was on call for heat to the tank is maintained at a certain temp, not without a call for heat. I think I'm starting to split hairs here and I'm sure there won't be any or enuf gravity to make a difference it's just how it shows to install them in their manual.
-
01-03-2013, 07:16 PM #21
Regular Guest
- Join Date
- Aug 2011
- Location
- Denver PA
- Posts
- 22
Are u going to insulate?
-
01-19-2013, 12:30 PM #22
Professional Member
- Join Date
- Feb 2006
- Posts
- 507
the board is mounted to an interior wall. there were no plans to insulate. i agree, it's a lot of copper but you have to realize too that this is a really old building downtown and there is no insulation in the walls. honestly, when comparing to the previous system, this new system will save the building owner tons.
-
02-19-2013, 09:15 PM #23
Professional Member
- Join Date
- Aug 2008
- Location
- levittown, pa
- Posts
- 58
I do not like ball valves on expansion tanks, but thats me. Very nice work though! I get laughed at for painting floor heat manifolds red and blue.