01-06-2013, 09:30 PM #14
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,757
They appear to be 10" OD flex pipes. That's about 1,000 cfm, (flex is more restrictive to the airflow) or 600 cfm short. Based on the blowers capabilities, 1,600 cfm of return air (at .08 static) is desired.
-
01-06-2013, 09:32 PM #15
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,757
-
01-06-2013, 09:35 PM #16
Regular Guest
- Join Date
- Sep 2012
- Location
- GA
- Posts
- 306
Thanks for the information. I'll measure to make sure sometime. We do plan to replace the furnace next winter and we want to downsize, but since the heat pump is 3.5 tons, we'll still have to have a furnace with a 4 ton blower installed. Hopefully we can find a GOOD company to install the furnace and redo the ductwork as necessary. I don't think the company who installed the heat pump did a manual j. The old A/C was a 3.5 ton as well.
-
01-06-2013, 09:37 PM #17
Regular Guest
- Join Date
- Sep 2012
- Location
- GA
- Posts
- 306
-
01-06-2013, 09:40 PM #18
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,757
-
01-06-2013, 09:42 PM #19
Regular Guest
- Join Date
- Sep 2012
- Location
- GA
- Posts
- 306
That's okay. I knew what you meant anyways.