Results 1 to 13 of 21
    Dec 2012
    90% Carrier has rich gas exhaust?
    Need help
    Dec 2011
    San Antonio, TX
    Need more info!
    Chicago, IL
    Secondary heat exchanger is likely plugged.
    S.E. Pa
    you need to provide some intelligible data on this. What were the combustion analysis numbers and what is the appliance doing or not doing? How did you come to this conclusion? By *rich* what do you mean?
    Nov 2012
    Craig1 is probably correct, but you need a flue gas analysis. You needto know how much co is in the exhaust.
    May 2011
    The usual amount is 'higher PPM than my TPI is capable of reading'.
    Dec 2012
    If what I think you’re talking about is true I would also suspect a clogged secondary. I encountered many carriers with clogged secondary’s and the symptoms were always the same, awful smell at exhaust, extremely high ppm on my combustion analyzer.
    Dec 2012
    OK relax, here is some data. Found 4 inch filter very plugged (removed), supply temp. at 100 degrees, return temp. 70 degrees, factory spec is 40-70 delta T. Found gas manifold pressure at 3.5 inch water column. Took CO reading in house and readings were 0. Did not take readings out at exhaust. (Stupid) Did notice pressure tape fitting on gas valve on manifold side connected to combustion fresh air intake.
    Dec 2012
    Thanks for the help!! Will return and take CO readings on exhaust and let you all know the results!!
    In a machine room
    Does the exhaust have a bad smell? Or what led you to believe it was rich?
    Dec 2012
    Customer was complaining, and when I arrived I could smell it. Then I went over to the exhaust and it just smelled rich to me. Hope that helps.
    Dec 2012
    Just took CO readings and it was off the scale, so i am a commercial HVAC guy, can you give me an idea how hard it is to change out a secondary heat exchanger and time involved?? (Still waiting to hear back from Carrier about warranty details)
    May 2012
    Upper Michigan
    I wouldn't bother replacing the secondary, they changed there design because it was so problematic. Last one I found with bad secondary they gave like 500 or 1500 towards a new furnace I think.
    That one smelled terrible on lp.
