When setting up Board assignments what is the .1 or .2 ? Example: Board 8 Point 5 ( what is the third number bd 8 pt 5,4) ?
Thanks,
-
12-26-2012, 05:40 AM #2
The first number is the Comm Module.
1,2,3 This is set by using the rotary switches on that board.
Since multiple boards can be connected to each comm module, the second number identifies the specific board.
The third number identifies the point on that specific board.
-
12-26-2012, 06:54 AM #3
So if I have a 5 1.1 it would be com 5 bd 1 pt 1 ?
-