    Danfoss AK255

    When setting up Board assignments what is the .1 or .2 ? Example: Board 8 Point 5 ( what is the third number bd 8 pt 5,4) ?

    Thanks,

  2. #2
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,400
    The first number is the Comm Module.

    1,2,3 This is set by using the rotary switches on that board.

    Since multiple boards can be connected to each comm module, the second number identifies the specific board.

    The third number identifies the point on that specific board.

  3. #3
    Join Date
    Apr 2010
    Location
    Richmond, Virginia
    Posts
    311
    So if I have a 5 1.1 it would be com 5 bd 1 pt 1 ?

  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,400