Page 2 of 2 FirstFirst 12
Results 14 to 21 of 21
  1. #14
    Join Date
    Jan 2002
    Location
    East Grand Forks, MN
    Posts
    1,378
    Post Likes
    Quote Originally Posted by tostaos View Post
    Let's look at my situation two weeks ago. I have a 3.5 t AC that is running just fine and doesn't need replacement, which makes it irrelevant that I don't know if the AC is slightly oversized or not. I will need a 4 ton blower. I have 2 sizes of furnace available, a 80k and a 100k btu. I know that the 80k furnace is large enough as the old furnace heated the house just fine. So for what reason would I run a heat load calculation that will tell me that the optimal size would be a 70k furnace?
    It tells more than this.

    1. Heatloss tells me what capacity I need for heating...
    2. Heatloss tells me what amount of air flow I need...
    3. Heatgain tells me what amount of airflow I need...
    4. Sensible HG tells me what capacity I need for cooling...
    5. It helps me determine how much fresh air I need...
    6. It tells me the square footage and approximate leak rates I have...
    7. It tells me the correct size of the duct system...

    And it takes me just one hour to accomplish all this...

    Even if I determined that the AC system is oversized, I still would install the correct furnace capacity for the house (output of heat and airflow regardless of
    the AC system). I would not size a furnace based on the size of an existing AC system; this would be a no no for me and for the customers.

    The existing system does not dictate what should be installed!! (I hate guessing: my warranties can not exist with chance).

  2. #15
    Join Date
    Jan 2005
    Location
    Littleton, CO
    Posts
    271
    Post Likes
    I perform a load calc on every install that I perform. Not a lot that I can do about the bad duct work from the 80's and the gravity systems. With that said I berform a static test on the existing equipment to see how the current air flow is. If air is low maybe change some duct work, turning vanes, variable speed motor, etc to get the proper airflow by utilizing the lower BTU of the furnace, as long as it works with the load calc.
    Become a friend or fan on Facebook

  3. #16
    Join Date
    Nov 2012
    Location
    Charlotte, Michigan 48813
    Posts
    144
    Post Likes
    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.
    Last edited by jpsmith1cm; 12-27-2012 at 07:02 PM. Reason: non AOP member

  4. #17
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,674
    Post Likes
    taxman

    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.

  5. #18
    Join Date
    Nov 2005
    Location
    Brownbakistan
    Posts
    4,529
    Post Likes
    Quote Originally Posted by arc8 View Post
    It tells more than this.

    1. Heatloss tells me what capacity I need for heating...
    2. Heatloss tells me what amount of air flow I need...
    3. Heatgain tells me what amount of airflow I need...
    4. Sensible HG tells me what capacity I need for cooling...
    5. It helps me determine how much fresh air I need...
    6. It tells me the square footage and approximate leak rates I have...
    7. It tells me the correct size of the duct system...


    Even if I determined that the AC system is oversized, I still would install the correct furnace capacity for the house (output of heat and airflow regardless of
    the AC system). I would not size a furnace based on the size of an existing AC system; this would be a no no for me and for the customers.

    The existing system does not dictate what should be installed!! (I hate guessing: my warranties can not exist with chance).
    You do the right thing as you are obviously not smart enough to distinguish when a load calc is necessary or not.

  6. #19
    Join Date
    Jan 2002
    Location
    East Grand Forks, MN
    Posts
    1,378
    Post Likes
    Quote Originally Posted by tostaos View Post
    You do the right thing as you are obviously not smart enough to distinguish when a load calc is necessary or not.
    Doing the right thing is the smart move no matter what men may say or do.

    May you be smart to know the difference..

    Godspeed.

  7. #20
    Join Date
    Jun 2007
    Location
    Minneapolis, MN
    Posts
    1,016
    Post Likes
    You are right on all counts. A proper heat load separates the amateur from the professional and a condensing furnace will be the best buy for the residential heating for some time to come in most markets.

  8. #21
    Join Date
    Nov 2005
    Location
    Brownbakistan
    Posts
    4,529
    Post Likes
    Another one who needs a pat on his back. lol... and some reading lesson combined with some abstract thinking.
    BTW I do a heat load calculation on 95% of my installs.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.