Results 1 to 10 of 10
  1. #1
    Join Date
    Dec 2012
    Posts
    3
    Post Likes

    Adjusting IDF motor pulley to FLA ratings of RTU

    Hello,

    For years I've adjusted IDF motor pulleys to the FLA ratings of the blower motor with the theory of I'm loading my evap coil up more and getting the system to its peak performance. I've had techs tell me I was incorrect with this but never offer any true explanation as to why. So am I right with doing this and making an improvement in the system, or am I incorrect in doing this? The systems work fine when I do this with no complains, I just felt I was making a system better by doing so. I know I wont dehumidify as well increasing my airflow over the evap coil, but I felt I am loading the coil up more, hence removing more heat from the space. I just want to have some educated opinions on this... Thanks...

  2. #2
    Join Date
    Jul 2003
    Location
    Orange County N.Y.
    Posts
    1,180
    Post Likes
    Quote Originally Posted by Brraapp26 View Post
    Hello,

    For years I've adjusted IDF motor pulleys to the FLA ratings of the blower motor with the theory of I'm loading my evap coil up more and getting the system to its peak performance. I've had techs tell me I was incorrect with this but never offer any true explanation as to why. So am I right with doing this and making an improvement in the system, or am I incorrect in doing this? The systems work fine when I do this with no complains, I just felt I was making a system better by doing so. I know I wont dehumidify as well increasing my airflow over the evap coil, but I felt I am loading the coil up more, hence removing more heat from the space. I just want to have some educated opinions on this... Thanks...
    I will set up a pair of sheaves/pulleys to run FLA only on initial start up. Then someone needs to do some air balancing, because someone designed the system to run at whatever CFM through each register and that's what it should have.

    Other than that the sheaves when replaced get set up the same as the originals, where I hope that somewhere in the past there was a air balancing done to the system.

    Just make sure that the customer doesn't have any issues with the increased noise if you do decide to increase the airflow. For your own peace of mind if nothing else, other than the callback you might get.

    ...Ron
    Roof Rat

  3. #3
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,029
    Post Likes
    Quote Originally Posted by Brraapp26 View Post
    ...I know I wont dehumidify as well increasing my airflow over the evap coil...
    that is the problem isn't it? sure, you may get a greater load on the coil, but you may not satisfy the humidity conditions as well. the thermostat will satisfy but the humidity may be too high. to account for this, your customer may lower the thermostat setting to a much lower temperature to make the ac run longer. this will cause the system to use more energy. your customers may not complain to you, but their bills may be going up. on the flip side, you slow the air flow down and you don't satisfy the thermostat or cause the coil to freeze. it is a fine line some days.
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  4. #4
    Join Date
    Oct 2009
    Location
    Raleigh, NC
    Posts
    845
    Post Likes
    You have to make sure you are taking readings with the panels on as well. A forward-inclined blower will unload at higher static.

  5. #5
    Join Date
    Sep 2006
    Location
    Ohio
    Posts
    675
    Post Likes
    You need to set it up for the design CFM of the unit and the space.

  6. #6
    Join Date
    May 2007
    Location
    Dry as a bone Tucson
    Posts
    4,841
    Post Likes
    Quote Originally Posted by hands View Post
    You need to set it up for the design CFM of the unit and the space.
    Name:  RPMs.jpg
Views: 566
Size:  17.9 KB
    "Christ is the Son of God Who died for the redemption of sinners and was resurrected after three days. This is the greatest truth in the universe. I die because of my belief in Christ."
    Watchman Nee



  7. #7
    Join Date
    Dec 2012
    Location
    Daphne, AL
    Posts
    79
    Post Likes
    I would definitely set the blower for the design airflow. Airflow is the first thing I like to confirm otherwise most other measurements and data collection is meaningless, somewhat.

  8. #8
    Join Date
    Mar 2010
    Location
    Morgan Hill Ca.
    Posts
    1,398
    Post Likes
    I am going to try to respond to your post without using my first prick card of the year.. Bear with me.


    Quote Originally Posted by Brraapp26 View Post
    Hello,

    For years I've adjusted IDF motor pulleys to the FLA ratings of the blower motor with the theory of I'm loading my evap coil up more and getting the system to its peak performance.
    You are 100% incorrect in adjusting the IFM to FLA... There are literally dozens of reasons why.

    Quote Originally Posted by Brraapp26 View Post
    I've had techs tell me I was incorrect with this but never offer any true explanation as to why.
    Just because they don't have the exact terminology does not make them any less right...


    Quote Originally Posted by Brraapp26 View Post
    So am I right with doing this and making an improvement in the system, or am I incorrect in doing this?
    In most cases you will be "hurting" performance more than "improving" it...


    Quote Originally Posted by Brraapp26 View Post
    The systems work fine when I do this with no complains, I just felt I was making a system better by doing so. I know I wont dehumidify as well increasing my airflow over the evap coil, but I felt I am loading the coil up more, hence removing more heat from the space.
    You could be loading the coil less....

    Some of the reasons for not doing this practice;

    Condensate carryover due to coil face velocity
    Major loss of latent performance
    Potential loss of filter performance
    If it is a gas pack, loss of heat performance
    Potential of over speeding the blower wheel causing damage to the unit
    Excessive noise
    Premature failures of the heat exchanger
    Potential overloading of the DX system

    The performance is measured using CFM, not fan HP. Do the math. You are taking the lazy way out.





    Quote Originally Posted by Brraapp26 View Post
    I just want to have some educated opinions on this... Thanks...
    If you read the installation and maintenance manuals supplied with your machines, you will immediately understand that what you are doing is fundamentally wrong... Willing to bet nowhere in the O and M does it state "adjust the blower speed to the full load amperage of the blower motor". Why do you think that is?

    Hope this was both constructive and insightful.

    GT
    If a day goes by and you have learned nothing, I hope you got a lot of sleep.

  9. #9
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,623
    Post Likes
    While you may be increasing the sensible capacity of the unit, you are also decreasing the latent capacity. And in some buildings that will cause them to set the stat lower and make them use more electric.

    The factory original blower motor in a unit is selected to meet and exceed the units CFM requirements at rated TESP. And should only need to be running at FLA when the duct design is restrictive enough that the TESP is above the units rated TESP.

    Look at the fan charts/data for the units you are working on. You'll see they often are moving the CFM they need at amp draws under the FLA of the motor.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  10. #10
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Fan curve for sure, although everyone I work with adjusts based on amps. We don't even have a tach....

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.