gas fireplace, where is the thermocouple?
Went on a call today for a blazeking pegasus 9300. Pilot won't stay lit. I removed the logs to gain access to pilot assy. The assy. only has a pilot hood, ignitor and a thermopile. What on this system holds the pilot valve open? Is the ignitor also a flame sensor? Does a thermopile ever double as pilot and main valve control?
-
12-23-2012, 06:47 PM #2
Professional Member*
- Join Date
- Aug 2012
- Location
- willowick ,oh
- Posts
- 192
Powerpile holds your pilot. Check voltage from powerpile to the valve
-
12-23-2012, 07:06 PM #3
Thread relocated to the "Fireplace" section of the site.
-
12-24-2012, 08:53 AM #4
Yes, the thermopile performs both the pilot safety and the main operator functions. There are many things that could be wrong here:
low inlet gas pressure
dirty pilot burner orifice
clogged primary air holes in pilot burner
pilot burner flame diverters not adjusted to TP
vent obstruction
logs out of place
secondary air ports in burner obstructed
poor connections
faulty snap discs in safety circuit
wiring faults in Th-Tp/TH circuit including faulty switch or too many switches (max 2), non-millivolt type thermostat (and that is only if this unit is listed for a stat)
Best left up to those familiar with servicing hearth appliances.Keep the fire inside the fireplace.
-
12-24-2012, 09:24 AM #5
The thermopile does ,you can test it by milivolts. Your range will be 500 -700 milivolts good.
Regards