    got a question,
    if a filter should be at least 1 square foot per ton, why does goodman have a filter holder in its unit, 5 ton air handler, 20 by 22 or 440 sq inches compared to the needed 720

  2. #2
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    5,271
    Originally posted by doneinnc
    got a question,
    if a filter should be at least 1 square foot per ton, why does goodman have a filter holder in its unit, 5 ton air handler, 20 by 22 or 440 sq inches compared to the needed 720
    Do you mean
    any other MFg may have a larger filter?
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art".

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  3. #3
    Join Date
    May 2004
    Location
    Rapid City, SD
    Posts
    7,385
    One quick answer $$$

    For what it's worth, most filters that come in a furnace (or AHU) will be marginal or undersized. Heck, a lot of the filters that are installed in designated filter racks are not exactly over sized! *sorry, you caught me on a bad day... I actually did a clean and check today on a 100,000 BTU furnace today with a 14x20 filter, and at least 2" of it was sticking out of the drop.
    "If you call that hard work, a koala’s life would look heroic."

    VETO PRO PAC, The Official Tool Bag of HVAC-Talk.com

    Testo... you guys rule!

  4. #4
    Join Date
    Dec 2006
    Posts
    5
    no but I wonder if the goodman unit will work properly

  5. #5
    Join Date
    Aug 2006
    Location
    Florida (some where) way-south
    Posts
    226
    got a question,
    if a filter should be at least 1 square foot per ton, why does goodman have a filter holder in its unit, 5 ton air handler, 20 by 22 or 440 sq inches compared to the needed 720

    answer:
    Hey dude
    the filter size the unit bring will work properly.

    besides how much space do you think the airhandler will take.
    for 720 sq in. it will be king size filter 20 x 36 just what you need in your closet. J.K.

    the 20x22x1 is good enough
    doing one call at a time.


  6. #6
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Originally posted by doneinnc
    no but I wonder if the goodman unit will work properly

    You should size the ducts and filter for the actual install,per Manual D ,from ACCA.

    Factory supplied filters in the air handler aren't very restrictive ,us the fan data chart from the mfr. and Manual D.Don't use a 3M type one inch pleated in the air handler filter slot,it's too restrictive.


  7. #7
    Join Date
    Mar 2004
    Posts
    1,042
    Goodman specs typically show double the filter area for disposable filters as for "permanent" filters. The only permanent filter I know of has a hard time even catching hair, though, so it's not very restrictive.

    For five ton furnaces their spec is 960 square inches of "disposable" filter, but 480 square inches for "permanent".

    Hmm... if they stopped including those worthless internal filter racks, would hacks do better work, or would they just leave the filters off completely? :-D

    Either way it takes a heck of a lot of filter area to stay under the typical 0.5"/0.8" ESP limit. Not many people ever measure that, though, to know that they're always over.

  8. #8
    Join Date
    Nov 2005
    Posts
    354
    where does manuel d say what size filter to use?

  9. #9
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Originally posted by iowa tech
    where does manuel d say what size filter to use?
    It lists recommended velocities and you use the actual PD of the filter to determine the ASP and resulting Friction Rate to select ducts with the ductolator.

  10. #10
    Join Date
    Nov 2005
    Posts
    354
    should you use same asp for supply and return

  11. #11
    Join Date
    Nov 2005
    Posts
    104
    Where did you get 1 sqft per ton? I have never heard of that. Thats not going to apply to the bottom of the unit, maybe to the grill size. Its all about static pressure and velocity not the size of the opening in the unit. Many manufacturers use the same cabinet for different btu units.

    "Hey home depot you got any of those 27x38 filters in for my 4.5 ton yet?"

  12. #12
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    5,271
    Originally posted by duxinaroe
    Where did you get 1 sq.ft. per ton?

    Thats not going to apply to the bottom of the unit, maybe to the grill size.
    400 Feet Per Minute ( FPM ) is
    appropriate for filter GRILLE sizing.

    A.K.A.
    1 Square Foot / Ton
    for Wall or Ceiling filters.
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art".

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  13. #13
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Originally posted by iowa tech
    should you use same asp for supply and return

    The ASP is determined by Manual D,current method would yield the same ASP for supply as return.

    If an existing and space for new or unable to enlarge ducts ,you could use a different ASP for return or supply.This would mean you'd have larger ducts on one,so space would need to be avalable for that.