12-26-2012, 08:21 PM #14
For the Ghetto landlords I just put a fan cycle control on the fan to cycle it off and on to controlhead preasure. I had one last 6 Years on a CPU room till it started screaming and people complained. Scroll compressor also.
If they don't wanna pay to do it right just make sure they know what they are getting upfront.
-
12-27-2012, 05:28 PM #15
Professional Member*
- Join Date
- May 2011
- Location
- Ripley, WV
- Posts
- 838
I was thinking about one of those external crank case heaters that wrap around the compressor and tighten up like a hose clamp. Instead of being used on a compressor install it on the accumulator and set to energize when the contactor closes. Also include a temperature sensor to keep it from coming on when ambient temperatures are close to design specs.
-
12-27-2012, 08:53 PM #16
Regular Guest
- Join Date
- Jan 2008
- Location
- s chester county,pa
- Posts
- 140
I would use a manufacturer specd low ambient kit only. if not maybe use an economizer control.
-
12-27-2012, 08:59 PM #17
Thanks for the tips guys. I think I might try a fan cycle switch. I'll call up Johnstone tomorrow and see what they have. So what does it do, do you run the hot from the fan through this switch and hook up some kind of shraeder tee to the liquid line service port and it cuts power to the fan when the head pressure is too low and turns on the fan when it gets up to the proper range?
America; first we fight for our freedom,
then we make laws to take it away.
-Alfred E Newman
-
12-27-2012, 09:03 PM #18To the man who always did it right. I love you dad and I will miss you to much for words.
Stay Thirsty My Friends
Support the Skilled Trades Don't DIY
-
12-27-2012, 10:53 PM #19
Professional Member*
- Join Date
- Feb 2009
- Location
- Tallahassee, FL
- Posts
- 4,705
That unit have a fancy motor on it? Not ecm is it?
-
12-28-2012, 04:59 PM #20
Professional Member*
- Join Date
- May 2011
- Location
- Ripley, WV
- Posts
- 838
-
12-28-2012, 06:13 PM #21
Professional Member*
- Join Date
- Feb 2009
- Location
- Tallahassee, FL
- Posts
- 4,705
-
12-28-2012, 09:46 PM #22
Probably is an ECM on a super SEER unit. A fan cycle kit probably could cycle the 240v constant supply but the module may not put up with that for long. If York says don't do it, they would know.
Yes, it is ECM.
-
12-28-2012, 11:17 PM #23
It is an ECM. I tried to install an ICM low ambient control on another heat pump before and couldn't get it to work. I followed the directions and also called their tech support line but it wouldn't go. Would a cut in/out work on the ECM? I would imagine it would.
America; first we fight for our freedom,
then we make laws to take it away.
-Alfred E Newman
-
12-29-2012, 07:15 AM #24
An ECM is wired hot. Low voltage signal tells it to come on. I suppose you could put a fan cycle kit in the 240v always hot feed but the constant cycling could be hard on the motor or the module. I would have a chat with a York tech rep before risking it.
-
12-30-2012, 05:47 PM #25
-
12-30-2012, 06:19 PM #26
Regular Guest
- Join Date
- Jun 2001
- Location
- Moore, Oklahoma
- Posts
- 2,674
Why not use a relay to cycle the low voltage signal?