    Compressor Noise During Low Ambient Cooling

    I went on a call where a customer was having compressor noise issues with his York 18 SEER heat pump in cooling mode at low outdoor temperatures. I haven't had much experience with cooling at low ambient, I seemed to be able to reduced the noise a bit by raising the head pressure. If low temps are indeed the cause of the noise, is there an easy way to boost head pressure? I tried to install a low ambient kit a while back to slow fan speed but was either too stupid to make it work, or the equipment might not have been compatible.
    America; first we fight for our freedom,
    then we make laws to take it away.

    -Alfred E Newman

  2. #2
    Join Date
    Jan 2007
    Location
    Stongsville Oh
    Posts
    1,410
    Post Likes
    Was it a scroll compressor and 410a refrigerant? They do get louder with low head.
    ckartson
    I didn't write the book I just read it!

  3. #3
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Customer is concerned about high energy bills so he buys a 18 seer AC. Wont open windows on a cool day....

  4. #4
    Join Date
    Jun 2011
    Location
    Seattle WA
    Posts
    1,253
    Post Likes
    Thread Starter
    Yes it is a scroll with 410a. Opening windows won't do. He works for the university and does some sort of plant research. He's got a space with some pretty decent heat load from high powered lights that run year round (and no it's not weed haha). Any help for me guys?
    America; first we fight for our freedom,
    then we make laws to take it away.

    -Alfred E Newman

  5. #5
    Join Date
    Jun 2011
    Location
    Seattle WA
    Posts
    1,253
    Post Likes
    Thread Starter
    Double post
    America; first we fight for our freedom,
    then we make laws to take it away.

    -Alfred E Newman

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    That unit is not designed to be used with any type of head control. It says that in the install instructions.

    Sounds like you are getting flood back. Might want to see if you can increase the indoor blower speed to evaporate more of the refrigerant.

  7. #7
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    could installing a crank case heater help this problem?

  8. #8
    Join Date
    May 2011
    Location
    Ripley, WV
    Posts
    1,607
    Post Likes
    Would putting a heater on the accumulator(if equipped) be an option to speed up the boiling off of excess refrigerant? Just have one on the compressor that energizes on contactor open and one on the accumulator that energizes when the contactor closes.

  9. #9
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    Don't think liquid flood is the issue here. I hope you have a txv indoors. Even then with low ambient the valve should be wide open and still have higher than design SH due to ultra low head.

  10. #10
    Join Date
    Jan 2005
    Location
    Akron
    Posts
    1,815
    Post Likes
    I have heard a pinging noise/rattle when there is not enough pressure difference across the compressor. The scrolls will start to separate. Happens when the head is to low and the indoor air temp to high. The high efficiency of the coil becomes to high. The equipment might be outside of its design specifications.
    JLB,

  11. #11
    Join Date
    Jun 2011
    Location
    Seattle WA
    Posts
    1,253
    Post Likes
    Thread Starter
    This unit has a factory installed crankcase heater. There is also an indoor TXV. Beenthere, I will try to increase blower speed, its certainly worth a shot. Ron, thats an interesting idea. Do they even make such a heater? Jim, I'm afraid you're probably right. At this point I'm just trying to figure out a way to raise the head pressure without getting too ghetto... Thanks for the replies fellas
    America; first we fight for our freedom,
    then we make laws to take it away.

    -Alfred E Newman

  12. #12
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    What type of low ambient did you try ?

  13. #13
    Join Date
    Nov 2008
    Location
    baltimore
    Posts
    26
    Post Likes
    A common fan cycle switch would work to control head pressure. Johnson sells a bunch of models compatiable with 410a. A hot gas bypass could also help problem with solenoid to close bypass in heating mode. A combination of both might help as well.

  14. #14
    Join Date
    Feb 2012
    Location
    Toronto Canada
    Posts
    1,090
    Post Likes
    For the Ghetto landlords I just put a fan cycle control on the fan to cycle it off and on to controlhead preasure. I had one last 6 Years on a CPU room till it started screaming and people complained. Scroll compressor also.

    If they don't wanna pay to do it right just make sure they know what they are getting upfront.

  15. #15
    Join Date
    May 2011
    Location
    Ripley, WV
    Posts
    1,607
    Post Likes
    Quote Originally Posted by LibertyTree View Post
    This unit has a factory installed crankcase heater. There is also an indoor TXV. Beenthere, I will try to increase blower speed, its certainly worth a shot. Ron, thats an interesting idea. Do they even make such a heater? Jim, I'm afraid you're probably right. At this point I'm just trying to figure out a way to raise the head pressure without getting too ghetto... Thanks for the replies fellas
    I was thinking about one of those external crank case heaters that wrap around the compressor and tighten up like a hose clamp. Instead of being used on a compressor install it on the accumulator and set to energize when the contactor closes. Also include a temperature sensor to keep it from coming on when ambient temperatures are close to design specs.

  16. #16
    Join Date
    Jan 2008
    Location
    s chester county,pa
    Posts
    157
    Post Likes
    I would use a manufacturer specd low ambient kit only. if not maybe use an economizer control.

  17. #17
    Join Date
    Jun 2011
    Location
    Seattle WA
    Posts
    1,253
    Post Likes
    Thread Starter
    Thanks for the tips guys. I think I might try a fan cycle switch. I'll call up Johnstone tomorrow and see what they have. So what does it do, do you run the hot from the fan through this switch and hook up some kind of shraeder tee to the liquid line service port and it cuts power to the fan when the head pressure is too low and turns on the fan when it gets up to the proper range?
    America; first we fight for our freedom,
    then we make laws to take it away.

    -Alfred E Newman

  18. #18
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes
    Quote Originally Posted by LibertyTree View Post
    Thanks for the tips guys. I think I might try a fan cycle switch. I'll call up Johnstone tomorrow and see what they have. So what does it do, do you run the hot from the fan through this switch and hook up some kind of shraeder tee to the liquid line service port and it cuts power to the fan when the head pressure is too low and turns on the fan when it gets up to the proper range?
    They have those the cut in and out. You could also get one that slows down the fan motor. ICM makes a few off them. They are easy to install since you do not have to mess with refrigerant connections.


    Sent from my iPad using Tapatalk HD
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  19. #19
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    That unit have a fancy motor on it? Not ecm is it?

  20. #20
    Join Date
    May 2011
    Location
    Ripley, WV
    Posts
    1,607
    Post Likes
    Quote Originally Posted by SBKold View Post
    That unit have a fancy motor on it? Not ecm is it?
    Good question, I've seen some low ambient kits that specify they are for use on ball bearing motors only.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •