    Carrier 80% furnace consistently running a high heat rise.

    Not quite 1 year old Carrier single-stage 80-percenter, 66k BTU. Can't recall the model and serial. The house is an older 1100 sq. ft. ranch with a single return in the hall and two more in bedrooms.

    Unit was consistently going out on primary limit. I found the temperature rise to be well over 80F when I first got there. 40-70 is the correct range.

    After verifying the correct blower speed setting and that the capacitor was good, I checked the gas pressure. Was set at 3.7"wc. I pulled it back to 3.2". Data tag says 3.2 to 3.8. A-coil was only three years old, and clean. Venting was fine. And it wasn't the vent limit switch that was tripping.

    The filter is a 16x20 pleated that was new. There was also a patch panel over a roughly 10x10 hole on the drop where a humidifier used to be. I pulled both of those just out of curiosity to see what I would get. Temp rise dropped to a bit over 70. Still high, though.

    I think the return duct is a contributor to the problem. The bottom of the drop is basically a 16x16x20 box with the filter in it. There's a 16x8 drop on top of that. On one side of the drop, there's 8" round that goes off to a single return (can't tell exactly how far - basement is finished). On the other side of the drop, 16x10 ductwork goes about 8 feet, making two 90-degree turns in the process, before it stops and another several feet of 8" round connects to the panning for the other two returns.

    I'm only describing the ductwork from memory. And I'm sure my descriptions of it sound goofy...I'm greener than green on the whole tin side of things.

  2. #2
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,249
    Post Likes
    Quote Originally Posted by Andr00 View Post
    Not quite 1 year old Carrier single-stage 80-percenter, 66k BTU.
    Unit was consistently going out on primary limit. I found the temperature rise to be well over 80F when I first got there. 40-70 is the correct range.
    After verifying the correct blower speed setting and that the capacitor was good
    What is the correct blower speed setting? The one set by the manufacturer?

    This unit needs to be moving about 860 cfm of air (130 cfm/10k btuh) in the heating mode.

    Did you have a chance to do a static pressure test, or use some other means of verifying the airflow? My guess is you are probably pushing .8 - 1.0" wc. in this system.

    As an example - the carrier 58STX070 (66k btuh, 40-70ºf temp rise) with a 2 ton blower, will only move 870 cfm on the high speed tap at 0.5" wc. On the med-low speed tap, it is only moving 595 cfm of air at 0.5" wc.
    Last edited by rundawg; 12-23-2012 at 08:59 AM. Reason: typo
    Instead of learning the tricks of the trade, learn the trade.

  3. #3
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by Andr00 View Post
    I think the return duct is a contributor to the problem..
    Pull the blower door and run it that will answer that question.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  4. #4
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    I've found these carrier units sensitive to low airflow, especially when the furnace is oversized. 66k for 1100 sq ft is oversized unless the house is in Alaska, 50% glass, or leaks like a sieve. The solution is to repair the marginal ductwork and returns or install a 44k furnace that has the same size blower.

  5. #5
    Join Date
    Jun 2000
    Location
    N. W., IN
    Posts
    1,021
    Post Likes
    In my neighborhood with houses as described (like mine) that furnace works just fine after I've done some improvement to the return duct.

  6. #6
    Join Date
    Jun 2012
    Location
    Rising Sun, Maryland, United States
    Posts
    111
    Post Likes
    Quote Originally Posted by rundawg View Post
    What is the correct blower speed setting? The one set by the manufacturer?

    This unit needs to be moving about 860 cfm of air (130 cfm/10k btuh) in the heating mode.

    Did you have a chance to do a static pressure test, or use some other means of verifying the airflow? My guess is you are probably pushing .8 - 1.0" wc. in this system.

    As an example - the carrier 58STX070 (66k btuh, 40-70ºf temp rise) with a 2 ton blower, will only move 870 cfm on the high speed tap at 0.5" wc. On the med-low speed tap, it is only moving 595 cfm of air at 0.5" wc.
    I totally agree here ive had a few where i hadto bump up to high speed to get more air flow across the heat exchanger.cause it would trip the high limit

  7. #7
    Join Date
    Jun 2004
    Location
    Eugene, Oregon
    Posts
    1,015
    Post Likes
    You need to move more air. Increase the fan speed if possible. If it's not possible to increase fan speed you'll need to increase your duct size to move more air. Most likely the return is undersized. Measure the external static pressure to determine where the most restriction is located.
    "The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin
    "Don't argue with an idiot, they will drag you down to their level and beat you with experience". --Mark Twain
    http://www.campbellmechanical.com

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •