01-18-2009, 09:18 PM #14
Not with the condenser below the evap.
There is a trap requirement.
But, not like you think.
-
01-18-2009, 09:32 PM #15
No return.
- Join Date
- Jul 2006
- Location
- NW burbs of Detroit
- Posts
- 6,058
Just looked it up. According to a Copeland piping reference manual every ten feet to avoid liq or oil slugging which may remain in the evap. Also suggested the use of liq line solenoid.
-
01-18-2009, 09:41 PM #16
OK, so.. ...
I appreciate the help, but in a sort it's open ended. I do not want to walk away from this one. I feel as if these people have been taken. They are asking for new equipment, I'm not a salesman (not in this case) I am a service man. I will reference the Copeland specs. and I would greatly appreciate the trap information that I am misled on. Thank you , overscore23
-
01-18-2009, 09:42 PM #17
Long line set applications like this.
Its better to call the unit manufacturer.
They are the ones that have to honor the warranty(or will void it) after the compressor manufacturers 18 month warranty expires(36 months I think if its a 10 year comp warranty).
On special piping applications(this one qualifies) its best to draw a diagarm and fax, or email it to the manufacturer(fax is better, then you get the engineers signiture on it when they fax it back). And go by their recomendation.(Remember, if you don't have the name of who approved it, then it was never approveded).
That way, you have proof, that you followed their recomendations.(keeps warranty in tact)
Trapping an over sized vapor line, can cause more harm then it prevents.
-
01-18-2009, 09:50 PM #18
No return.
- Join Date
- Jul 2006
- Location
- NW burbs of Detroit
- Posts
- 6,058
what's a few comps between friends.
-
01-18-2009, 09:56 PM #19
Hey thanks.
-
01-18-2009, 09:56 PM #20
No return.
- Join Date
- Jul 2006
- Location
- NW burbs of Detroit
- Posts
- 6,058
-
01-18-2009, 09:56 PM #21
-
01-18-2009, 10:13 PM #22
Nordyne is going to love that call, but I'll do it. I do feel more secure with a signature of a engineer backing whatever plan I go with. Thanks I appreciate your time.
-
01-18-2009, 10:17 PM #23
Have mod numbers available, and line sizes.
They may also want to know type of Metering device.
-
01-18-2009, 10:22 PM #24
Ok, thanks so what part of the country are you in ? I guess you guys get all areas and walks of life right ? I only ask because I am wondering how the economy has effected your area, I have a brother in law in Texas says work is so plentiful it's like they never new anything about recession depression mumbo jumbo, not in Missouri, it's a little rough, how bout your self ?
-
01-18-2009, 10:31 PM #25
No return.
- Join Date
- Jul 2006
- Location
- NW burbs of Detroit
- Posts
- 6,058
-
01-18-2009, 10:36 PM #26
Is the heat pump located 130' above the indoor coil? I have not seen line sizing charts yet for R410. It seems to me that if the vetical is a suction riser that there should be a trap every 20'. Also tonage may have needed correction due to line losses.